[Dsg-halla_magnets] PLC I/O module communication errors solved
Pablo Campero Rojas
campero at jlab.org
Mon Feb 8 18:22:16 EST 2021
Hi Steve,
I noticed that the communication between the PLC and the 1794-ACN15 Flex I/O Adapter module was finally without errors, but the PLC I/O fault indicator in RSLogix-5K software was still present due to communication issues with the MVI-94 ASCII Communication module.
I've proceeded to solve the issues by changing the configurations (connection node number) and rescheduling the ControlNet network for the MVI-94 ASCII communication module.
All I/O faults for the PLC are solved now, and the new PLC program with the changes done can be found at M:\dsg-halla_controls folder; the name of the ACD file is Cleo_V2_Feb_8_2021.
We can discuss more details about this matter during our next SoLID Magnet Controls meeting.
-Pablo