[Dsg-halla_magnets] SoLID Magnet- Voltage Taps readout cables

Steven Lassiter lassiter at jlab.org
Fri Jul 9 15:22:55 EDT 2021


For brief voltage spikes they should be okay.

the total voltage across the magnet is 350V, since the voltages are split the dataforths should only see 175V each for a short period

Steven.
________________________________
From: Brian Eng <beng at jlab.org>
Sent: Friday, July 9, 2021 3:19 PM
To: Pablo Campero Rojas <campero at jlab.org>; Steven Lassiter <lassiter at jlab.org>; dsg-halla_magnets at jlab.org <dsg-halla_magnets at jlab.org>
Subject: Re: [Dsg-halla_magnets] SoLID Magnet- Voltage Taps readout cables

Hi Steve,

For the voltage tap cables we were using the assumption that the max voltage during a quench would be 350VDC, hence the 600 VDC rated cables.

According to their data sheet, the dataforth signal conditioners are only rated to 240VAC or ~170 VDC for the input.

https://www.dataforth.com/catalog/pdf/scm5b30_31.pdf



Is there some sort of voltage division after the resistor box we're missing/not seeing?

________________________________
From: Dsg-halla_magnets <dsg-halla_magnets-bounces at jlab.org> on behalf of Pablo Campero Rojas <campero at jlab.org>
Sent: Friday, July 9, 2021 3:04 PM
To: Steven Lassiter <lassiter at jlab.org>; dsg-halla_magnets at jlab.org <dsg-halla_magnets at jlab.org>
Subject: Re: [Dsg-halla_magnets] SoLID Magnet- Voltage Taps readout cables

The voltage output range of the Dataforth module is -10 V to + 10 V, I guess that rating to 40 V the cables from the Dataforth to the the PLC terminal is just to be on the safe side.

What about my second question. Do we need to read/monitor the voltage taps for voltages greater than 40 V?


________________________________
From: Steven Lassiter <lassiter at jlab.org>
Sent: Friday, July 9, 2021 2:36 PM
To: Pablo Campero Rojas <campero at jlab.org>
Subject: Re: [Dsg-halla_magnets] SoLID Magnet- Voltage Taps readout cables

Hi  Pablo,

The signal conditioners will clamp at 40V so any wiring upstream of the dataforth needs to be rated higher, from the dataforth to the PLC terminal strip can be 40V.
40V rating is also all that is require of any wring after the dataforth, like from the PLC terminal strip to the I/o module.

Steven
________________________________
From: Dsg-halla_magnets <dsg-halla_magnets-bounces at jlab.org> on behalf of Pablo Campero Rojas <campero at jlab.org>
Sent: Friday, July 9, 2021 2:31 PM
To: dsg-halla_magnets at jlab.org <dsg-halla_magnets at jlab.org>
Subject: [Dsg-halla_magnets] SoLID Magnet- Voltage Taps readout cables

Hello Steven,

We are trying to determine the gauge size and voltage rating for the cables that connects the voltage tap signals from the terminal strip to the Dataforth signal conditioning modules  (see attached screenshot for Dwg A00000-16-03-0250 Voltage Tap Wiring Diagram, e.g. cable #250-01), but first we need to know what is the voltage expected in these cables?

Based on the Dataforth module's specs (model: SCM5B31-09D), the voltage input range is from -40 V to +40 V, if the expected voltage (e.g. during a quench event) is greater than 40 V, we will monitor only 40 V and not the actual voltage value. Is this the correct setup to monitor the voltage taps?


-Pablo

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-halla_solid/attachments/20210709/8e628ff2/attachment-0002.html>


More information about the Dsg-halla_magnets mailing list