[dsg-halla_solid] CLEO connectors
Steven Lassiter
lassiter at jlab.org
Sun Dec 11 17:08:43 EST 2022
Hello Pablo,
The Voltage tap connector at the end of the cable coming from the control rack to the resistor box is configured incorrectly. It seems that pins were used in a socket connector.
See attached photo.
This needs to be corrected asap so that the complete circuit can be made up and the quench detector channels tuned.
Also, some of the temperature sensors should be masked on the HMI screens as they will not be used.
We discussed this on Friday.
The following temperature sensors had issues that prevents them from being used in a four wire configuration or not all.
TS_6
TS_24
TS_9
TS_7
TS-33
Heidi is working on recovering as many as she can. These sensors were tested and found to be viable at the 25 pin connectors and then through to the 10 pin connectors. Somewhere between the 10 pin connectors and the I/O channel, the wires are either open or mis-wired.
I have updated the excel spreadsheet and the.acd file over the weekend. Will send the excel file to you on Monday.
Steven