[Dsg-dc] [Revised Logentry] DC Gas Mix flow setpoint
mcmullen at jlab.org
mcmullen at jlab.org
Fri Jan 26 15:40:05 EST 2018
Logentry Text:
--
The Mix 1 and 2 high flow set points multipliers have been decreased from 5 times the demand flow, down to 1.5 times the demand. During an unusually cold early January, the high flow set points were increased from 1.2 to 5 in order to reach 80 psi in the mix tanks. This week the high flow set points were reduced from 5 to 2 times the demand, both tanks were able to reach 80 psi. The multipliers have been further reduced to 1.5, this will be monitored to ensure that the system will be able to stay within the pressure band (60 to 80 psi) before reducing it back to 1.2 times the demand flow.
---