Hi Whit,
The control pressure is measured by the transmitter in psig, which is then converted to mbar in software. According to the manufacturer it has a fixed 14.7 psi (so ~1013.529 mbar) offset. If the set point is at 90 mbar it is really ~1103.529 mbar.
The ambient pressure sensor readout that is being displayed got stuck, rebooting it got the values updating again. The EPICS PV that ALERT is using is B_SYS_WEATHER_FC_L1:Press2 in case you wanted to monitor it directly/separately.
Let me know if there’s any other questions.
Brian
On Jan 15, 2025, at 12:34 PM, Marc Mcmullen via dsg-hallb_gas <dsg-hallb_gas at jlab.org> wrote:
Hi Bob, I’m out sick. So I’m forwarding this tho the group. Brian can probably look into it.
Also I looked and the input flow to MFC 308 is set to 20 sccm. Maybe change that to 167 sccm.
Marc
Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Bob Miller <rmiller at jlab.org>
Sent: Wednesday, January 15, 2025 11:20 AM
To: Armstrong, Whitney R. <warmstrong at anl.gov>; Marc Mcmullen <mcmullen at jlab.org>
Subject: Re: AHDC gas control
Hi Whitney,
I will refer this question to Marc, as he wrote the controls.
Bob Miller
Hall B Lead Engineer
(757) 822-9586
________________________________
From: Armstrong, Whitney R. <warmstrong at anl.gov>
Sent: Wednesday, January 15, 2025 10:44 AM
To: Bob Miller <rmiller at jlab.org>
Subject: [EXTERNAL] AHDC gas control
Hi Bob,
I have a question about the gas control system. When the alert gas set point is set to 90 mbar, what is that relative to in order to provide stable absolute pressure?
Also, the ambient pressure readout appears to not change and is at a value of 1017.54.
Thanks,
Whit
Whitney Armstrong
Assistant Physicist
Physics Division
Building 203
Argonne National Laboratory
9700 S. Cass Ave. | Argonne, IL 60439
630-252-5112 | 717-341-1080 mobile
warmstrong at anl.gov
_______________________________________________
dsg-hallb_gas mailing list
dsg-hallb_gas at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallb_gas
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_gas/attachments/20250115/d5bb82a0/attachment-0001.html>
More information about the dsg-hallb_gas
mailing list