We met a couple of weeks ago and discussed a better strategy to supply
CO2 to the detector in the hall. Currently, we use a mass flow
controller, which in the case of an outage which would outlast the UPS
would close. The solution is to change this to a mass flow transducer on
the detector inlet, which would be supplied by a standard rotameter
installed in the gas shed. This set up would then supply gas in any
condition and still be adjustable without entering the Hall.
The rough estimate for the new equipment would be approximately $3200
which would include one transducer, plus a spare, and a rotameter.
George is preparing an dollar figure quote and augmenting the drawings.
Once you receive the quote from us, please let us know how to proceed
with the procurement as soon as possible.