Hi Bob,
I have connected the H2O sensor to the Gas Controls, the initial readback value was ~2000 ppm and steadily dropping. In less than 20 minutes it has decreased to around 1100 ppm, and was still dropping.
If possible it would be helpful if we could run some gas from the supply tank directly through the transducer so we could have a baseline for reference. We also need to establish the return H2O set point, which will close the hall supply solenoid. Currently, the solenoid is unplugged from the AC relay.
This will be ready for use as soon as I can do some testing and update the FC cRIO software. I'll coordinate that with you and the RC.
-Marc
________________________________
From: Bob Miller <rmiller at jlab.org>
Sent: Monday, February 11, 2019 9:15 AM
To: Brian Eng; Marc Mcmullen
Subject: LTCC Gas H2O is Installed
Hi Marc and Brian,
The H2O sensor is installed and cabled.
The system is working fine now. I will have to wait for warmer weather
tomorrow to fill up sector 3.
Thanks,
Bob
--