Please find the LTCC purifier drawing and controls description attached.
The peer review consisted of:
* reviewing the drawing
* discussing the procedures and modes of operation
* reviewing the failure analysis
Specific topics discussed
* use a 250 lpm MFC for the N2 return
* move the MFM to the inlet of the purifier
* provide the option to recirculate the gas through the purifier to cool the condensate tank
* locate a temperature probe TT2042 with 2 separate temperature sensors
* if this is not available, add a 2nd temperature probe on the N2 discharge piping
Regards,
Bob
--
Bob Miller
Hall B Lead Engineer
Jefferson Lab
757 822-9586
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-ltcc/attachments/20190222/8fe6746a/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: B00000-01-12-PD03-Model RPM Purifier.pdf
Type: application/pdf
Size: 76534 bytes
Desc: B00000-01-12-PD03-Model RPM Purifier.pdf
URL: <https://mailman.jlab.org/pipermail/dsg-ltcc/attachments/20190222/8fe6746a/attachment-0001.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: LTCC Purifier Controls.docx
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 23142 bytes
Desc: LTCC Purifier Controls.docx
URL: <https://mailman.jlab.org/pipermail/dsg-ltcc/attachments/20190222/8fe6746a/attachment-0001.docx>
More information about the Dsg-ltcc
mailing list