[Dsg-hallb_magnets] Hall B Solenoid PSU issues
    Ruben Fair 
    rfair at jlab.org
       
    Wed Apr 26 09:37:26 EDT 2017
    
    
  
Thank you Pablo. 
Ruben 
From: "Pablo Campero Rojas" <campero at jlab.org> 
To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org> 
Cc: "Sarin Philip" <philip at jlab.org>, "Mark Todd" <mtodd at jlab.org> 
Sent: Wednesday, April 26, 2017 9:04:40 AM 
Subject: Re: [Dsg-hallb_magnets] Hall B Solenoid PSU issues 
Hello Ruben, 
Yesterday afternoon the problem with the PSU was solved. 
The PSU remote crate display was showing an interlock, which was occurring because of their interlocks inputs were not activated. These inputs are provided from the relay outputs of the PLC. 
The following steps were followed to solve the problem: 
1.Verify interlock hardwiring for the PSU crate board; used drawings B000000900-0639 and B000000900-0654. 
2. Notice that PLC relay outputs that are wired to the interlock inputs of the PSU remote crate has to be always ‘ON’ to avoid the interlocks. 
3. Added PLC code in ‘ Magnet Interlocks’ routine to have always active the relay outputs (Slot 1- Remote PLC chassis) and match with the wiring mention above. 
4. Two PLC tags were added to the PLC routine: PLC_FAST_DUMP_BACKUP and PLC_SLOW_DUMP at channels 12 and 13 respectively. 
All changes in the Solenoid PLC were made Online, and latest version is running in the PLC controller. 
Best Regards 
Pablo Campero 
The following is a new meeting request: 
Subject: 	Hall B Solenoid PSU issues 
Organizer: 	"Ruben Fair" <rfair at jlab.org> 
Location: 	Hall B Level 2 - by solenoid PSU 
Time: 	Tuesday, April 25, 2017, 1:15:00 PM - 2:15:00 PM GMT -05:00 US/Canada Eastern 
Invitees: 	campero at jlab.org; mtodd at jlab.org; spiegel at jlab.org; philip at jlab.org; ghoshal at jlab.org 
*~*~*~*~*~*~*~*~*~* 
Pablo, 
We will need you there to possibly make changes to the PLC settings. 
Regards 
Ruben 
_______________________________________________ 
Dsg-hallb_magnets mailing list 
Dsg-hallb_magnets at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170426/f9eea878/attachment-0001.html>
    
    
More information about the Dsg-hallb_magnets
mailing list