[Dsg-hallb_magnets] I and C Related Torus Punch List Items

Tyler Lemon tlemon at jlab.org
Tue Jan 17 07:57:23 EST 2017


Hello Ruben and Nick, 

The new PT100s in the Torus relief valves had not been added to the LV cRIO. The program has now been updated to include the sensors. 

If all is clear, I will deploy the updated program that includes the six new PT100s this morning. 

Best regards, 
Tyler 


From: "Ruben Fair" <rfair at jlab.org> 
To: "Nicholas Sandoval" <sandoval at jlab.org> 
Cc: "Probir Ghoshal" <ghoshal at jlab.org>, "Tyler Lemon" <tlemon at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Wesley Moore" <wmoore at jlab.org>, "Scot Spiegel" <spiegel at jlab.org>, kashy at jlab.org 
Sent: Friday, January 13, 2017 5:13:38 PM 
Subject: Re: I and C Related Torus Punch List Items 

Excellent! 

Scot - when will you get the hardware for the PT? 

Tyler - I presume you will check the cRIO for the relief valve temps? 

Have a good weekend everyone 

Ruben 

> On Jan 13, 2017, at 5:01 PM, Nicholas Sandoval <sandoval at jlab.org> wrote: 
> 
> Hi Ruben, 
> 
> Just a quick update for you: 
> 
> 1. The new pressure transducer(PT8571) has been mapped in PLC/EPICs, Probir and I routed the cable. Scot still needs hardware for the calibration T manifold etc. 
> 
> 2. Probir and I confirmed that the flag lead platinum temperature readout and SSR heater control. Then Probir relabled the cables and I made the change in the PLC. I owe Scot a redlined copy of the dwg so he can update. 
> 
> 6. Relief Valve Temperature sensors were all terminated by Mark, Probir ohmed out the sensors and they read correct. Probir had to fix the wiring on one redundant sensor. cRIO is not updating the array and needs to be checked. 
> 
> 9. The ESR fail signal was moved to "Warnings (not interlocked)" category on EPICs interlock GUI and removed from PLC interlock sum. 
> 
> 10. Ramp Down fail was moved to "Warnings (not interlocked)" category on EPICs interlock GUI and removed from PLC interlock sum. 
> 
> Best Regards, 
> 
> Nick 
> 
> ----- Original Message ----- 
> From: "Ruben Fair" <rfair at jlab.org> 
> To: "Probir Ghoshal" <ghoshal at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>, "Wesley Moore" <wmoore at jlab.org>, "Scot Spiegel" <spiegel at jlab.org>, "Tyler Lemon" <tlemon at jlab.org>, "Krister Bruhwel" <bruhwel at jlab.org> 
> Cc: "Dave Kashy" <kashy at jlab.org>, "Ernest Stallworth" <stallwor at jlab.org>, "Joseph Matalevich" <josephm at jlab.org>, "Bob Miller" <rmiller at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org> 
> Sent: Friday, January 6, 2017 9:19:55 AM 
> Subject: I and C Related Torus Punch List Items 
> 
> Gentlemen, 
> 
> Please ensure that all the following I and C related Torus Punch List items are completed by 16th Jan 2017 unless otherwise stated. 
> 
> There are other punch list items which Dave and I are progressing separately. 
> 
> 1. Implement a lead flow solenoid vent through SV8122 (2 minutes) upon high return pressure with insufficient reduced lead flow (Alarm/warming should activate), cable needed 
> Please work with Scot Spiegel to define and fabricate the cable. (Nick, Dave, Scot) 
> 
> 2. Check all of lead flow controllers/lead heaters and TD121A/B temperature sensors AND be sure they are consistent with Voltage taps on same leads 
> Work with Probir to do this. (Nick, Probir) 
> 
> 3. Complete all electrical wiring diagrams and submit to the system for approval (Scot) 
> 
> 4. Implement and test digital filtering within cRIO FPGA to reduce iso-amp noise (Tyler, Nick, Probir) 
> Tyler - Nick suggested that it might also be an idea to move all the scaling calcs (and perhaps unit conversion calcs) to the FPGA to reduce the load on the cRIO processor? 
> See if it makes sense to do that. 
> You and Probir will need to run tests of course to ensure all the scaling is still correct. 
> And if the noise level has truly been reduced, then Probir and Nick will need to reassess the voltage threshold limits that we are currently using. 
> 
> 5. Automate warning beacons (Krister) - by 27th Jan 
> 
> 6. Check that the three temperature sensors (PT100s) on the relief valves on the TST are cabled up, cables are routed to terminal blocks and LV chassis (or Cryocon), LabVIEW (if via the LV chassis) has been updated, PLC code has been updated and these sensors are displayed on the EPICS helium screen. (Probir / Nick/ Wesley) 
> 
> 7. Update alarm handler to use the on-call cell phone no. provided by Doug, 757 748 5048 Sprint (Wesley) 
> 
> 8. Mount and wire up remaining three PT100 sensors to the relief valves on the magnet. Ensure the cables are labeled correctly. (Krister) - by 27th Jan 
> 
> 9. Remove requirement for controlled ramp down of magnet on ESR 'fail' signal (Nick) 
> 
> 
> Regards 
> 
> Ruben 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170117/1fbc9f59/attachment.html>


More information about the Dsg-hallb_magnets mailing list