[Dsg-hallb_magnets] Tested Vaporizer instrumentation
Brian Eng
beng at jlab.org
Wed Jul 26 17:19:11 EDT 2017
We also tested and confirmed that the 3 solenoid Cryo-con units will cause the EPICS screen to indicate a failure when the unit loses power.
However, if the on/off button is pushed on the units it won't cause an error because the units will still be alive on the network and return the last read temperatures, but the values will never change.
--
Brian Eng
Detector Support Group
757-269-6018
> On Jul 26, 2017, at 5:13 PM, Pablo Campero <campero at jlab.org> wrote:
>
> Hello Ruben,
>
> Brian and I tested the following instrumentation:
>
> - solenoid valve SV8678DV
> - solenoid valve SV8678CR
> -Temperature sensor TP8675
>
> Wiring, PLC logic and EPICS readouts were tested and verified . No observation during the test for the mentioned instrumentation, everything worked as we expected.
> Detailed information about the test can be found in the 'Instrumentation TEST PLC- EPICS PLAN_v8_July 26th 2017' spreadsheet.
>
> To complete with the test for the instrumentation on the vaporizer panel we still need to test valve SV8675BY (Pneumatic valve now), but 120V AC power will be required.
>
>
> Best Regards,
> Pablo