Ok we'll have to discuss this next week then
> On Jun 16, 2017, at 6:40 PM, Wesley Moore <wmoore at jlab.org> wrote:
> 
> Ruben,
> 
> It's kind of the opposite actually. Everything is supposed to be named the same, unless it's on the same PLC.  Then the PLC logic and EPICS-side works as a copy-paste of the torus. There are still plenty of differences, but it reduces the amount of work quite a bit. Just puts stricter restrictions on the naming. 
> 
> Wesley
> 
> 
> -------- Original message --------
> From: Ruben Fair <rfair at jlab.org> 
> Date: 6/16/17 5:34 PM (GMT-05:00) 
> To: wmoore <wmoore at jlab.org> 
> Cc: Pablo Campero Rojas <campero at jlab.org>, dsg-hallb magnets <dsg-hallb_magnets at jlab.org> 
> Subject: Re: Solenoid Controls_Final_Wiring check-out 
> 
> 
> Weren't they changed to refer to the solenoid?
> 
> 
> From: "wmoore" <wmoore at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "Pablo Campero Rojas" <campero at jlab.org>, "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Friday, June 16, 2017 5:21:29 PM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
> 
> Pablo,
> 
> They aren’t working because the tag names don’t match.  Why were they changed from:
> 
> CryoCon_Reset_PB
> CryoCon_WatchDog
> 
> Since they are coming from the Solenoid PLC, they shouldn’t need “Sol_”, right?
> 
> Wesley
> 
> On Jun 16, 2017, at 5:02 PM, Ruben Fair <rfair at jlab.org> wrote:
> 
> Thank you all
> 
> Wesley
> 
> Let us know when these issues are resolved.
> 
> Regards
> 
> Ruben
> 
> On Jun 16, 2017, at 4:54 PM, Pablo Campero <campero at jlab.org> wrote:
> 
> Hello Ruben,
> 
> Tyler, Amanda and I tested the following instrumentation:
>  
> 1. PT-100  temperature sensor TP8675 (Vaporizer)
> 2. PT-100 temperature sensor TP8680 (Relief Valve)
> 3. Cryocon Units 2 and 3.    
> 4. Solenoid valve SV8622 (Vent valve)   
> 
> Controls for the temperature sensors and solenoid valve are working as expected, and also readouts of these instrumentation was checked.
> Detailed information of the results for this test can be find in the TEST PLC- EPICS PLAN_v7_June 16th 2017 spreadsheet. Find it on M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
> 
> 
> Wesley,
> During the test, the 'Solenoid Cryocon Status' EPICS screen was checked too, and we noticed the following:
> 1. 'Solenoid Watchdog'  indicator is not updating  for Solenoid and DBX. (pink color in the Solenoid-Watchdog readout box)
> 2. 'Reset Button' is not connecting with the associate tag in the Solenoid PLC code.
> 
> Here is the tag names used in the Solenoid PLC code that are related with these signals mentioned above.
> 
> PLC TAG	Data Type 
> Sol_CryoCon_Reset_PB	BOOL
> Sol_CryoCon_Watchdog	INT
> 
> If you have a chance, please check and let me know any comments.
> 
> 
> Best Regards,
> Pablo 
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero Rojas" <campero at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Tuesday, June 13, 2017 8:58:13 AM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
> 
> Thank you very much Pablo - appreciate it.
> 
> Let me know if you need help.
> 
> Cheers
> 
> Ruben
> 
> 
> From: "Pablo Campero Rojas" <campero at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Tuesday, June 13, 2017 8:56:19 AM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
> 
> Hello Ruben,
> 
> The Instrumentation  TEST PLC- EPICS PLAN_v6_June 13th 2017 spreadsheet was update with the new instrumentation that needs to be tested. You can find it on the link : M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
> 
> The test for the instrumentation, that was required by Scot for the PTS (Temperature Sensors), Cryocon units and solenoid vales will be complete by the end of this week, I will let you know once I complete the tasks.
> 
> Best Regards,
> Pablo 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero Rojas" <campero at jlab.org>
> Sent: Tuesday, June 13, 2017 7:51:22 AM
> Subject: Fwd: Solenoid Controls_Final_Wiring check-out
> 
> Pablo,
> 
> Please confirm that these additional tests have been added to your I and C test spreadsheet.
> 
> When are you planning to complete the tests?
> 
> If you need help from Nick, Scot or myself let us know.
> 
> Regards
> 
> Ruben
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Scot Spiegel" <spiegel at jlab.org>
> Cc: "Probir Ghoshal" <ghoshal at jlab.org>, "Renuka Rajput-Ghoshal" <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>
> Sent: Friday, June 9, 2017 4:12:09 PM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
> 
> Thank you Scot.
> 
> Pablo,
> 
> Can you add these tests to your overall I and C test spreadsheet and then plan to get them completed within the next 2 weeks?
> 
> Regards
> 
> Ruben
> 
> 
> From: "Scot Spiegel" <spiegel at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "Probir Ghoshal" <ghoshal at jlab.org>, "Renuka Rajput-Ghoshal" <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>
> Sent: Friday, June 9, 2017 3:13:30 PM
> Subject: Solenoid Controls_Final_Wiring check-out
> 
> All,
> 
> Mark Lester and I have completed the last few cable terminations in the Solenoid Racks.
> 
> The remaining devices will need to verified before the Solenoid arrives.
> 
> Test requirement for -  Valve solenoids (vaporizer) 24VDC (X) 3, PT's (X) 2 & CRYOCON #2, Channel D for Vaporizer temperature.
> 
> Best regards,
> 
> Scot Spiegel
> Sr. Technologist / Designer
> Physics / Hall D
> JSA Jefferson Lab
> 12000 Jefferson Ave.
> Bldg. 55 Rm. 1546-24
> Newport News, VA. 23606
> Ph. 757-536-5900
> Wk. 757-269-5900
> 
> 
> 