Logentry Text:
--
While Torus was ramping to zero A this morning, the controlled ramp down interlock for LHe Liquid Level for sensor LL8120DP tripped.
The interlock trip level was verified on the PLC to be 65% with a delay time of 1 second.
The archiver shows that LL8120DP dropped below 65% for ~1.4 seconds before returning to ~70%.
Since the liquid level reading is back within limits, the interlock was reset using the EPICS button.
---