[Dsg-hallb_magnets] [New Logentry] Re: Torus FastDAQ down
    Ruben Fair 
    rfair at jlab.org
       
    Tue Mar  6 18:34:50 EST 2018
    
    
  
Ok
> On Mar 6, 2018, at 5:44 PM, Brian Eng <beng at jlab.org> wrote:
> 
> I don't think it is networking because the point the cRIO is getting stuck at is before networking should even be required. Also networking is perfectly fine in safe mode, so it isn't something upstream of the cRIO (bad cable, switch, etc nor the hardware itself).
> 
> If I was forced to guess as the cause it would be that these particular series of controllers use a different type of flash storage compared to the others. You have to use special commands just to change settings where as on the others you just open an editor and change the files.
> 
> That would explain why safe mode works, but normal doesn't. However, I'm not sure how to explain how the 2 previous times it has recovered itself just by being powered off for an extended period of time.
> 
> We'll see what happens with this one in a day or two, also if the SVT cRIO recovers itself as it died also.
> 
>> On Mar 6, 2018, at 5:35 PM, Ruben Fair <rfair at jlab.org> wrote:
>> 
>> Brian
>> 
>> Is this some sort of networking issue with the CRIO devices do you think?
>> 
>> Ruben
>> 
>>> On Mar 6, 2018, at 5:30 PM, beng at jlab.org wrote:
>>> 
>>> Re: Torus FastDAQ down
>>> 
>>> Lognumber 3543526. Submitted by beng on Tue, 03/06/2018 - 17:26. 
>>> Logbooks:    HBTORUS
>>> Entry Makers:    campero
>>> References:    3543494 - Torus FastDAQ down
>>> 3477357 - Follow-up Re: Solenoid and Torus FastDAQ cRIOs cannot connect to network
    
    
More information about the Dsg-hallb_magnets
mailing list