    <div class="moz-cite-prefix">Maxime,<br>
      <br>
       See if you can get the people together for a show and tell. I
      would be interested in attending.<br>
      <br>
      Volker<br>
      <br>
      On 1/10/18 10:18 AM, mdefurne wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:f91e4518-b413-7d5d-bbd7-c426767940da@jlab.org">
      <meta http-equiv="content-type" content="text/html; charset=utf-8">
      <p>Dear all,</p>
      <p><u><b>Before all explanations, I want to emphasize that Maxence
            and I are not gas experts. So we are just explaining you
            what we did,why we think it seems to be safe to make another
            test of the mixing system with isobutane. We decline any
            responsability if something goes wrong and final approval to
            start using mixing system with isobutane must come from the
            JLab staff in charge of it.    </b></u><br>
      </p>
      <p>Last night with Maxence, we did the following procedure:</p>
      <p>- Closed all the valves.</p>
      <p>- Closed the manometer for the argon supply.</p>
      <p>From this state where everything is closed, we opened the valve
        in the rack on the isobutane line supply and then filled the
        line from the isobutane bottle to the upstream valve of MFCs
        with isobutane. The pressure was about 25psi (cannot be more
        precise since the heat tape was ON at 15% at that moment... when
        heat tape is warming, pressure is increasing in the line). <br>
        Then we closed the bottle and left the system in this state
        overnight, i.e. all the line insulated with heat tape around at
        15% filled with isobutane.</p>
      <p>This morning we went to purge the line. To do so, we first open
        the relief valve and then we open the one of the valves allowing
        to purge with argon the isobutane MFC line. It is important to
        first open the relief valve, otherwise isobutane will first flow
        in a line which is not insulated and condense within a few
        seconds. (you tried it yesterday evening and relief valve was
        then spitting liquid and gaz. So 30F with no insulation will
        make isobutane condensing quite fast.)</p>
      <p>So this morning, only gaseous isobutane was exiting the relief
        valve. Apparently it seems that isobutane is not condensing
        anymore. And once the relief valve is closed, pressure in the
        line stayed at 0 (With liquid in it, I would expect to have some
        pressure built in the line). I nevertheless insist on the
        "apparently" since the relief valve is not exactly on the
        isobutane line.</p>
      <p>  So, considering all this, I would <u><b>only recommend</b></u>
        to start testing the mixing system with isobutane again. But <u><b>final
            approval must be given either by a staff of JLab since this
            system is JLab responsability.</b></u></p>
      <p>If you want a demonstration of the test later today (because
        the mail might not be very clear without the rack in front of
        you), we can organize it. However, I have not a faintest idea
        about what the next test is to ensure that isobutane is gaseous,
        except going through one MFC (no need to start using both
        immediately and risk to lose both of them).</p>
      <p>Finally, 15% for the heat tape seems fine for ~30F. But
        temperature will get colder over the week end and next week. We
        might consider to run safe, i.e. testing again isobutane state
        as soon as we hit a new minimum of temperature.<br>
      </p>
      <p>Kind regards,</p>
      <p>Maxime<br>
      </p>