It looks like the WANTGAS PV went away first which is why the flows were set to zero, see the attached plots.
<div class=""><br class="">
</div>
<div class="">The mixing system was working as intended.</div>
<div class=""><br class="">
</div>
<div class=""><img apple-inline="yes" id="A27355C2-CD66-4BED-ACAC-B01C6C9D73A8" src="cid:ACE639F6-7359-4C23-8DDD-41D7BC933114@jlab.org" class=""><br class="">
<br class="">
<blockquote type="cite" class="">On Jan 8, 2019, at 9:15 AM, Marc Mcmullen <<a href="mailto:mcmullen@jlab.org" class="">mcmullen@jlab.org</a>> wrote:<br class="">
<br class="">
Hi Maxime,<br class="">
<br class="">
Is there a reason the Mix 2 gas flow request is set to 0? The mixing system is in "Automatic", if gas is required someone needs to provide a flow set point on the Saclay PLC.<br class="">
<br class="">
Thanks,<br class="">
Marc</blockquote>