    In normal operation the compressor will operate in automatic. There
    should be no issue with the compressor running at it's maximum set
    point. Lowering operating pressure also reduces the cooling capacity
    of the system due to a power outage.<br>
    <br>
    The receiver relief valve is set to 175 psi, it is not possible for
    the compressor to overpressure the receiver or panel.<br>
    <br>
    The 90 psi relief valve on the panel is to protect the glass flow
    meters from overpressure in case of pressure regulator failure.
    These reliefs do not see receiver pressure unless the regulators
    fail in what would be a worse case scenario. <br>
    <br>
    Resistance to flow in a gas line is linear with length. For a
    realistic test, 50 ft lengths should be used. We may find that 2
    tubes may be required per sector to maximize cooling flow.<br>
    <br>
    There are certain critical system design parameters that should be
    verified. These critical parameters all deal with the cooling flow
    capacities. IMO, the following should be measured in order to verify
    the system will work in the hall as expected when installed.;<br>
    -> Max cooling flow rate for 1 detector<br>
    -> Max cooling flow rate for 2 detectors<br>
    -> Max Power outage flow and time for 1 detector<br>
    -> Max Power outage flow and time for 2 detectors<br>
    -> Min Power outage flow and time for 1 detector<br>
    -> Min Power outage flow and time for 2 detectors<br>
    <br>
    George<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 8/15/2017 11:38 AM, Tyler Lemon
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:2089561222.3579521.1502811528523.JavaMail.zimbra@jlab.org">
      <div style="font-family: times new roman,new york,times,serif;
        font-size: 12pt; color: #000000">
        <div>Hello George,<br>
        </div>
        <div><br data-mce-bogus="1">
        </div>
        <div>Since it was a proof of concept test, we only went up to an
          output pressure of 75 psi. Also, the OSP says the pressure in
          the tank should be 80 psi so we did not want to go over 80psi
          in the event the compressor did not shut off right when its
          output pressure reached the set point. </div>
        <div><br data-mce-bogus="1">
        </div>
        <div>There are also relief valves on the gas panel that are
          rated for 90 psi. Since we know the compressor does shut off
          immediately when the output pressure set point is reached, we
          could set the output pressure to be 80 psi.<br
            data-mce-bogus="1">
        </div>
        <div><br data-mce-bogus="1">
        </div>
        <div>For the length of the 1/2" OD tube, in April, Amanda,
          Pablo, and I did a rough measurement on the Forward Carriage
          (FC) for how long cables should be. We measured that roughly
          110 feet would allow a cable to stretch from the location of
          the gas panel on the FC top deck to where RICH will be on the
          FC. I can go with Mindy to do a more precise measurement so we
          have a more precise length.<br data-mce-bogus="1">
        </div>
        <div><br data-mce-bogus="1">
        </div>
        <div>Best regards,<br data-mce-bogus="1">
        </div>
        <div>Tyler<br data-mce-bogus="1">
        </div>
        <div><br data-mce-bogus="1">
        </div>
        <div><br data-mce-bogus="1">
        </div>
        <div><br>
        </div>
        <hr id="zwchr" data-marker="__DIVIDER__">
        <div data-marker="__HEADERS__"><b>From: </b>"Amrit Yegneswaran"
          <a class="moz-txt-link-rfc2396E" href="mailto:yeg@jlab.org"><yeg@jlab.org></a><br>
          <b>To: </b>"George Jacobs" <a class="moz-txt-link-rfc2396E" href="mailto:jacobsg@jlab.org"><jacobsg@jlab.org></a><br>
          <b>Cc: </b>"dsg-rich" <a class="moz-txt-link-rfc2396E" href="mailto:dsg-rich@jlab.org"><dsg-rich@jlab.org></a><br>
          <b>Sent: </b>Tuesday, August 15, 2017 11:06:43 AM<br>
          <b>Subject: </b>Re: [Dsg-rich] RICH gas panel test results<br>
        </div>
        <div><br>
        </div>
        <div data-marker="__QUOTED_TEXT__">
          <div style="font-family: tahoma,new york,times,serif;
            font-size: 14pt; color: #009900"
            data-mce-style="font-family: tahoma,new york,times,serif;
            font-size: 14pt; color: #009900;">
            <div>hello george,<br>
            </div>
            <div>and here i was thinking you as the gas expert and would
              know all the answers or <em>find out these answers</em>,
              but apparently i was wrong.<br>
            </div>
            <br>
            <div>here, some comments.<br>
            </div>
            <br>
            <div>with regards to the length, since we know where the
              detector goes in the hall and where the compressor and air
              tank go,  i suggest you determine the length to the best
              of your ability.<br>
            </div>
            <div>100 ft was a good guess; also adequate length to run it
              around the clean room.<br>
            </div>
            <div>mindy please assist george in this endeavor. <br>
            </div>
            <br>
            <div>the goals of the test was <em>basically proof of
                principle that the system works.</em><br>
            </div>
            <div>we learned that the system does indeed work, but not
              100% as we expected.<br>
            </div>
            <br>
            <div>we learned that the wrong pressure gas was either
              ordered/delivered.<br>
            </div>
            <div>then there were the issues with connections/ fittings.<br>
            </div>
            <div>issues with cables.<br>
            </div>
            <div>we learned that the output N2 temperature was 68F to
              72F<br>
            </div>
            <div>we learned that the flow never quite reached 400 l/m<br>
            </div>
            <div>and so on and on...<br>
            </div>
            <br>
            <div>so we learned all the stuff which wasn't right and all
              the stuff that needed to be learned,<br>
            </div>
            <div><strong>one cannot know what one has to know before one
                knows it.</strong><br>
            </div>
            <div>or to quote amanda: i don't know what i don't know till
              i don't know.<br>
            </div>
            <br>
            <div>with regards to the compressor set point tyler will
              explain it to you.<br>
            </div>
            <br>
            <div>yes, there were two pre-test meetings on two
              consecutive wednesdays during the dsg meeting.<br>
            </div>
            <div>i was requesting <em>t<span style="text-decoration:
                  underline;" data-mce-style="text-decoration:
                  underline;">he test to demonstrate proof of principle
                  that the system works.</span></em><br>
            </div>
            <br>
            <div>so, the end<br>
            </div>
            <div>amrit<br>
            </div>
            <br>
            <br>
            <br>
            <br>
            <br>
            <br>
            <br>
            <hr id="zwchr">
            <div><b>From: </b>"George Jacobs" <a class="moz-txt-link-rfc2396E" href="mailto:jacobsg@jlab.org"><jacobsg@jlab.org></a><br>
              <b>To: </b><a class="moz-txt-link-abbreviated" href="mailto:dsg-rich@jlab.org">dsg-rich@jlab.org</a><br>
              <b>Sent: </b>Tuesday, August 15, 2017 8:53:43 AM<br>
              <b>Subject: </b>Re: [Dsg-rich] RICH gas panel test
              results<br>
            </div>
            <br>
            <div>I have a couple questions on the air cooling system
              test performed yesterday;<br>
              1) What is the length of the 1/2 OD line that goes from
              the air panel outlet to the RICH inlet? It started out as
              a 100ft length.<br>
              2) Absent a written test procedure, what were the specific
              goals of this test?<br>
              3) Why is the air compressor outlet pressure setpoint so
              far below the rated output of the compressor?<br>
              4) Was there a pre-test meeting or discussion prior the
              test?<br>
              <br>
              George<br>
              <br>
              <div class="moz-cite-prefix">On 8/14/2017 2:58 PM, Tyler
                Lemon wrote:<br>
              </div>
              <blockquote
                cite="mid:1735821927.3449471.1502737089499.JavaMail.zimbra@jlab.org">
                <div>
                  <div>
                    <div>
                      <div>
                        <div>
                          <div>Hello,<br>
                          </div>
                          <br>
                          <div>This morning Mindy, Marc, George, and I
                            tested the RICH gas panel. Both the nitrogen
                            purge instrumentation and air cooling
                            instrumentation were tested.<br>
                          </div>
                          <br>
                          <div>For the nitrogen purge system, we
                            connected the nitrogen dewar to the gas
                            panel. Initially, we were not able to get
                            over 4 liters per minute (L/min) of nitrogen
                            flow as the dewar was not a high-pressure
                            dewar, as ordered. George has already
                            arranged for the correct, high-pressure
                            dewar to be delivered on Wednesday August
                            16. After noting the dewar was a
                            low-pressure dewar, we swapped the installed
                             pressure regulator with an orifice for a
                            regulator without an orifice. The new
                            regulator without the orifice allowed the
                            nitrogen flow to be set to ~15 L/min. We set
                            the nitrogen flow to 6 L/min and measured
                            the temperature of the gas on the very end
                            of the gas line in EEL 124 cleanroom. The
                            output nitrogen temperature at the end of
                            the gas line was ~69 degrees Fahrenheit. The
                            ambient temperature of EEL 124 was ~72
                            degrees Fahrenheit.</div>
                          <br>
                          <div>For the air-cooling system, we connected
                            the air lines to the gas panel. We set the
                            compressor to automatically turn off if its
                            output pressure reached 70 psi and to
                            automatically turn on if its output pressure
                            drops to 58 psi. The values set on manual
                            instrumentation and the values measured by
                            the mass flow meter are in the table below.
                            To get the flow output to be higher, we had
                            to also increase the pressure to the
                            rotameter using the manual pressure
                            regulator.</div>
                          <br>
                          <div>
                            <table>
                              <tbody>
                                <tr>
                                  <td>Manual Pressure Regulator [psi]<br>
                                  </td>
                                  <td>Manual Rotameter [L/min]<br>
                                  </td>
                                  <td>Mass Flow Meter Measurement
                                    [L/min]<br>
                                  </td>
                                </tr>
                                <tr>
                                  <td>30<br>
                                  </td>
                                  <td>200<br>
                                  </td>
                                  <td>200<br>
                                  </td>
                                </tr>
                                <tr>
                                  <td>50<br>
                                  </td>
                                  <td>300<br>
                                  </td>
                                  <td>300<br>
                                  </td>
                                </tr>
                                <tr>
                                  <td><span>60</span><br>
                                  </td>
                                  <td><span>400</span><br>
                                  </td>
                                  <td><span>350</span><br>
                                  </td>
                                </tr>
                              </tbody>
                            </table>
                          </div>
                        </div>
                        <br>
                      </div>
                      <div>We were not able to get 400 L/min when the
                        manual rotameter was set to 400 L/min. We tried
                        increasing the output pressure at which the
                        compressor turns off from 70 psi to 75 psi, but
                        the pressure at the manual pressure regulator
                        did not go above ~60 psi and the measured flow
                        above ~350 psi. If during the cooling tests, 350
                        L/min is not enough to sufficiently cool the
                        electronic panel, we could further adjust the
                        output settings of the compressor to try to
                        reach 400 L/min.</div>
                      <br>
                      <div>Best regards,<br>
                      </div>
                      <div>Tyler<br>
                      </div>
                    </div>
                    <br>
                  </div>
                </div>
                <br>
                <fieldset class="mimeAttachmentHeader"></fieldset>
                <br>
                <pre>_______________________________________________
Dsg-rich mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-rich@jlab.org" target="_blank" data-mce-href="mailto:Dsg-rich@jlab.org" moz-do-not-send="true">Dsg-rich@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-rich" target="_blank" data-mce-href="https://mailman.jlab.org/mailman/listinfo/dsg-rich" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-rich</a>
</pre>
              </blockquote>
              <br>
              <pre class="moz-signature">-- 
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606

(office) 757-269-7115

(cell)   757-876-0480

(email) <a class="moz-txt-link-abbreviated" href="mailto:jacobsg@jlab.org" target="_blank" data-mce-href="mailto:jacobsg@jlab.org" moz-do-not-send="true">jacobsg@jlab.org</a>

(website) <a class="moz-txt-link-freetext" href="https://userweb.jlab.org/%7Ejacobsg" target="_blank" data-mce-href="https://userweb.jlab.org/~jacobsg" moz-do-not-send="true">https://userweb.jlab.org/~jacobsg</a>
</pre>
              <br>
              _______________________________________________<br>
              Dsg-rich mailing list<br>
              <a class="moz-txt-link-abbreviated" href="mailto:Dsg-rich@jlab.org">Dsg-rich@jlab.org</a><br>
              <a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-rich">https://mailman.jlab.org/mailman/listinfo/dsg-rich</a><br>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          Dsg-rich mailing list<br>
          <a class="moz-txt-link-abbreviated" href="mailto:Dsg-rich@jlab.org">Dsg-rich@jlab.org</a><br>
          <a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-rich">https://mailman.jlab.org/mailman/listinfo/dsg-rich</a><br>
        </div>
      </div>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606

(office) 757-269-7115

(cell)   757-876-0480

(email) <a class="moz-txt-link-abbreviated" href="mailto:jacobsg@jlab.org">jacobsg@jlab.org</a>

(website) <a class="moz-txt-link-freetext" href="https://userweb.jlab.org/~jacobsg">https://userweb.jlab.org/~jacobsg</a></pre>
  </body>
</html>