    <p>Hi Jeorge,</p>
    <p>you mentioned the two 10 mm ID internal supply lines and
      distribution manifolds internal to the detector, unfortunately the
      OD for these lines is 10 mm and not the ID.</p>
    <p>Best regards</p>
    <p>Sandro<br>
    </p>
    <br>
    <div class="moz-cite-prefix">Il 21/09/2017 16:54, George Jacobs ha
      scritto:<br>
    </div>
    <blockquote type="cite"
      cite="mid:933c2230-14c6-769c-8168-02085e306858@jlab.org">
      
      Hi Bob,<br>
      <br>
      The RICH air cooling pressure system does not include the air
      supply line from the valve panel to the RICH or the distribution
      manifolds inside the electronics module installed inside the RICH.
      Pressure in the internal distribution manifold could be as high as
      60 psi at full design air flow. Assuming a worse case scenario of
      the supply pressure regulator failure, it could be as high as 90
      psi.<br>
      <br>
      Plan is to run two 1" OD, 0.813" ID nylon tubes from the panel to
      the detector, L=60 ft each, to supply the two 10 mm ID internal
      supply lines and distribution manifolds internal to the detector,
      L=16 ft each. see attached diagram.<br>
      <br>
      The distribution manifold was designed by INFN and produced by a
      3D printer. These manifolds are questionable at best. I have
      suggested that these be replaced with a section of SS tubing that
      has the 2mm holes, orifices, drilled in it.<br>
      <br>
      The 1" OD Nylotube is rated at 230 psi. The 10mm ID tubing and
      10mm SS tubing are rated > 120 psi. All components have
      pressure rating greater than the worse case failure scenario.<br>
      <br>
      Due to the accelerated schedule, we should quickly determine a way
      forward to complete any remaining pressure system requirements.<br>
      <br>
      Thanks,<br>
      George<br>
      <pre class="moz-signature" cols="72">-- 
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606

(office) 757-269-7115

(cell)   757-876-0480

(email) <a class="moz-txt-link-abbreviated" href="mailto:jacobsg@jlab.org" moz-do-not-send="true">jacobsg@jlab.org</a>

(website) <a class="moz-txt-link-freetext" href="https://userweb.jlab.org/%7Ejacobsg" moz-do-not-send="true">https://userweb.jlab.org/~jacobsg</a></pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Dsg-rich mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-rich@jlab.org">Dsg-rich@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-rich">https://mailman.jlab.org/mailman/listinfo/dsg-rich</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
-----------------------------------------
Dr. Eng. Sandro Tomassini
Istituto Nazionale di Fisica Nucleare
Laboratori Nazionali di Frascati
---Research Division---
P.O.Box 13 00044 Frascati (RM) Italy
Tel. office: +39 06 9403 2919/8089
Fax: +39 06 94032256
e-mail: <a class="moz-txt-link-abbreviated" href="mailto:sandro.tomassini@lnf.infn.it">sandro.tomassini@lnf.infn.it</a>
<a class="moz-txt-link-freetext" href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.lnf.infn.it_&d=DwMCaQ&c=lz9TcOasaINaaC3U7FbMev2lsutwpI4--09aP8Lu18s&r=9YtCiIg5kE6YCo5iFAyFiMgzNCONVcBowotEOgGZ4Co&m=CGc8MNWKw9JWrZ1CHvjLbNXv3h3tebPBmmxTR1x1GI4&s=moLBtGB94NrqoISGh1qJhSn9xbO6JomCEi_uSlU89Gw&e=">http://www.lnf.infn.it/</a>
-----------------------------------------
-- </pre>
  </body>
</html>