[Dsg-rtpc] Fw: relief valve on non-flammable gas supply to gas panel
George Jacobs
jacobsg at jlab.org
Tue Apr 30 14:40:32 EDT 2019
--
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606
(office) 757-269-7021
(cell) 757-876-0480
(email) jacobsg at jlab.org
________________________________
From: George Jacobs
Sent: Tuesday, April 30, 2019 2:36 PM
To: Bill Crahen
Cc: Bob Miller
Subject: Re: relief valve on non-flammable gas supply to gas panel
Hi Bill,
OK, let's look at the valve position error scenarios. But first, let's look at the purpose of these valves.
The MV3, MV4, and MV5 manual valves permit gas flow bypass around the DMS, isolating the DMS so it can be removed if needed. MV3 is the DMS volume inlet, MV5 is the DMS volume outlet and MV4 is the DMS volume bypass. With MV4 opened and MV3 and MV5 closed, the DMS volume is isolated and the gas flow is bypassed directly to the RTPC and it's bubbler vent to atmosphere. Pressure cannot build up at the bubbler, the exhaust line is open to the atmosphere. Adding these valves also adds the potential for operator error.
Here is the scenario you were concerned with. This is an operator error scenario, improper valve lineup. MV3 is closed and MV4 and MV5 are opened. Since MV4 is now open, the gas flow is still connected to the RTPC volume and it's bubbler vent to atmosphere. This scenario is the same as during normal operation except the gas flow bypasses the inlet of the DMS volume. Since the RTPC bubbler vents to atmosphere, pressure cannot build up above that created by the 0.1" oil level. Again, pressure cannot build up at the bubbler, the exhaust line is open to the atmosphere.
Next scenario, MV3 and MV4 are closed. This scenario represents another operator error in the valve lineup. Here, gas pressure could increase in the line between the MFC and the MV3 and MV4 branches. This pressure could eventually equalize to the MFC gas supply pressure. The volume of tubing is quite small and the volume of the DMS and RTPC are >10 liters each.
Next, another operator error scenario, MV3 is open and MV4 and MV5 are shut. This is why the DMS has a bubbler connected directly to the gas volume via a 1 psi check valve. The check valve should be fully open at 3 psi. The oil prevents back flow of air into the gas volume.
The pressure regulator is not used as a safety device. It is sized such, that if an operator were to adjust it to maximum output, the pressure in the line would be below that of the relief valve setpoint. It's just a way to prevent inadvertent gas loss. It prevents an operator error from becoming a larger problem.
The items most likely to be damaged due to overpressure are the DMS and RTPC volumes. The most likely damage will result in an increase in leakage. All detectors leak at some level. Typically, all detector leak rates increases over time. If the detector leak rates are excessive, a larger MFC may be required if repairs are not practical or possible within the available window.
Cheers,
George
--
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606
(office) 757-269-7021
(cell) 757-876-0480
(email) jacobsg at jlab.org
________________________________
From: Bill Crahen <wcrahen at jlab.org>
Sent: Tuesday, April 30, 2019 11:09 AM
To: George Jacobs
Cc: Bob Miller
Subject: Re: relief valve on non-flammable gas supply to gas panel
George, I could close MV3 and open MV4 and MV5 and directly pressurize the bubbler. These bubblers are glass, and they will not be connected to a system that can potentially expose them to 75 psig. Another note- a regulator is not a safety device. The relief valve (in this case) determines the system design pressure. If it seems more reasonable, we could install reliefs on the lines going to the bubblers (which presumably should never see more than a few inches of water pressure).
On 4/30/2019 9:56 AM, George Jacobs wrote:
Hi Bill,
We should plan to meet and discuss this system once the panel arrives. Initial tests will be performed with out any detector volumes. Tests with detector volumes will be performed later, once the detectors are ready. Initial tests will be to verify MFC operation and transducer output.
I believe the MFC gas supply requirement specification is 10-40 psi. The pre-mix gas supply pressure regulator has a 0-50 psi output range. The MFC pressure rating is rated far higher, 1500 psi. Initial regulator setpoint should be 15 psi for testing.
The RTPC gas supply pressure system ends at the 3 valves, MV3, MV4, and MV6. There is no way to shut off gas flow downstream of these valves before it vents to atmosphere. Pressure cannot increase as the gas will simply vent to atmosphere via the RTPC bubbler.
The DMS and RTPC volumes are not capable of holding pressure. They are not pressure system componenets, nor are the oil filled bubblers. The oil filled bubblers will vent gas at ~0.1-0.2 inches water column or ~0.007 psi.
The current MFC maximum flow rate is 250 sccm. Even if the pressure regulator and MFC both fail open, the 0.017 orifice used on the high pressure side of the gas supply pressure regulators, limits gas flow to <10 slm.
The pressure transducers are capable of much higher pressure that the RTPC and DMS volumes can handle. Since the transducers are connected to the DMS and RTPC, and to the vent bubblers via the DMS and RTPC volumes, pressure cannot build beyond what is required to flow the < 10 slm flow to atmosphere in the worse case scenerio. The 10 slm flow is based on a multiple failure scenerio, ie the worse case, where both the gas supply pressure regulator and the MFC fail open.
The He4 gas supply flows to a He gas bag or balloon. The pressure in the bag is at most 1-2 inches water column, 0.07 psi, and limited by the bubbler oil level. Helium bag gas supplies are a very common setup in many experiments.
In my experience, low pressure relief valves tend to leak. There is also a potential problem using a relef valve with a setpoint lower than the max output of the gas supply pressure regulator. Improper pressure regulator setpoint can result in the rapid depletion of the gas supply. The gas has a 6 week lead time. So, we really don't want to go there.
Cheers,
George
--
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606
(office) 757-269-7021
(cell) 757-876-0480
(email) jacobsg at jlab.org<mailto:jacobsg at jlab.org>
________________________________
From: Bill Crahen <wcrahen at jlab.org><mailto:wcrahen at jlab.org>
Sent: Monday, April 29, 2019 3:49 PM
To: George Jacobs
Cc: Bob Miller; Carlos Ayerbe Gayoso
Subject: relief valve on non-flammable gas supply to gas panel
George- the last version of your P&ID I have from you shows a 75 psig
relief valve on both the premix and He cylinder regulators. The gas
panel has several components that would not be happy with that, namely
the pressure transmitters and the bubblers (which are glass). My
understanding is that you only need to supply a required minimum
operating pressure to the MFC (which is 10 psig).
If the relief valves had a 15 psig set point (McMaster Carr 4701K11,
ASME Sec VIII approved), at the flow rate your rotometer is set for and
the MFC rate would only lead to ~ 0.2 psi pressure drop for 300' of 1/2"
stainless tubing, so you could set the regulators at ~12 psig, which
gives you a 25% margin on the relief valve. Alternately, you could
install the relief at the gas panel (which might be wiser, as this low
pressure unit would not be susceptible to ice, etc.).
Everyone let me know your thoughts- Bill Crahen
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-rtpc/attachments/20190430/6338a2d9/attachment.html>
More information about the Dsg-rtpc
mailing list