    <p>Could you please provide update on this request, we are about to
      have beam and the cable from the hardware interlock box to the
      pump relay box is not yet installed. This could lead to the CVT
      down time due to the issues with circuit breaker I reported. Thank
      you<br>
    </p>
    <div class="moz-forward-container"><br>
      -------- Forwarded Message --------
      <table class="moz-email-headers-table" cellspacing="0"
        cellpadding="0" border="0">
        <tbody>
          <tr>
            <th valign="BASELINE" align="RIGHT" nowrap="nowrap">Subject:
            </th>
            <td>Re: [dsg-svt] Fwd: SVT Cooling System Trip Analysis
              (Hardware Interlock)</td>
          </tr>
          <tr>
            <th valign="BASELINE" align="RIGHT" nowrap="nowrap">Date: </th>
            <td>Fri, 10 Aug 2018 08:51:22 -0400</td>
          </tr>
          <tr>
            <th valign="BASELINE" align="RIGHT" nowrap="nowrap">From: </th>
            <td>Yuri Gotra <a class="moz-txt-link-rfc2396E" href="mailto:gotra@jlab.org"><gotra@jlab.org></a></td>
          </tr>
          <tr>
            <th valign="BASELINE" align="RIGHT" nowrap="nowrap">To: </th>
            <td>dsg-svt <a class="moz-txt-link-rfc2396E" href="mailto:dsg-svt@jlab.org"><dsg-svt@jlab.org></a></td>
          </tr>
        </tbody>
      </table>
      <pre>Today's trip is caused by the circuit breaker. Around 4 am I started 
warming up the tracker to prepare for the target alignment work. The 
chiller and the external pump are on the same 20 A breaker (connected 
via the relay). The chiller draws 15 A and the pump 3 A. When heater is 
operational there could be current jumps over 20 A. Bob requested 
separation of the pump and the chiller power which requires extra relay 
box. Could you please provide another relay box with additional control 
line from the hardware interlock box connected to the interlock system 
the same way as for the existing relay box. I believe splitting the same 
control line would do. Thank you
</pre>