[Dsg-hallc_controls] UPS status routine review
    Tyler Lemon 
    tlemon at jlab.org
       
    Wed Sep  5 07:50:34 EDT 2018
    
    
  
Hi Mike, 
Thanks for the feedback. Attached is the code screenshot with the OSRI replaced with a OSFI. 
Tyler 
From: "Mike Fowler" <fowler at jlab.org> 
To: "Tyler Lemon" <tlemon at jlab.org> 
Cc: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Tuesday, September 4, 2018 1:24:15 PM 
Subject: Re: [Dsg-hallc_controls] UPS status routine review 
Hi, 
In the SHMS routine the OSRI should be changed to a OSFI 
With the OSRI the timer will be reset when the fault is true, should be reset when not true. 
Mike 
On 9/4/2018 10:56 AM, Tyler Lemon wrote: 
Hi Mike, 
Attached are screenshots changing the code to your recommendations. 
Best regards, 
Tyler 
From: "Mike Fowler" <fowler at jlab.org> 
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Tuesday, September 4, 2018 8:17:27 AM 
Subject: [Dsg-hallc_controls] UPS status routine review 
Hi, 
Attached is my comments on the UPS status routine. 
Cheers, 
Mike 
_______________________________________________ 
Dsg-hallc_controls mailing list 
Dsg-hallc_controls at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180905/41ad4234/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SHMS UPS routine.PNG
Type: image/png
Size: 40351 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180905/41ad4234/attachment-0001.png>
    
    
More information about the Dsg-hallc_controls
mailing list