Well that didn't work.
Slot3:channels 14 and 15 are currently being utilized to monitor the status of the VFD controller.
Drawings need to be updated.
Back to searching for two available I/O channels
Steven
----- Original Message -----
From: "lassiter" <lassiter at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Wednesday, September 5, 2018 2:06:14 PM
Subject: wiring the UPS
Hi, 
The following I/O channels within the HMS rotation I/O chassis have been freed up and can be used for three UPS status. 
The UPS contacts should be dry contacts using the NO to common leg to indicate that the UPS is running off of its battery. No need for additional 24V voltage source as the I/O module will be in sourcing mode. 
HMS UPS goes to slot 3: Channel 13 wire up two wires to terminal strip TS-PLC-03 13.1 and 13.2 
PLC UPS goes to slot 3: Channel 15 wire up two wires directly to the I/O modules pins 31 and 32 (add the wire to the existing wire going into pin 32). 
The SHMS wiring will have to first go from the UPS, down through the detector hut floor, to the white rotation panel box, connect to terminal strip TS-VFD-01 to the empty side of terminals 22 and 23. The colors of the existing wires will be determined shortly. Then within the Rotation rack, the two wires coming from the TS-VFD-01 22 and 23 need to be wired to terminal strip TS-PLC-03 14.1 and 14.2. The SHMS will use slot:3 channel 14 of the rotation chassis. 
Thanks 