[Dsg-hallc_controls] Cable put in counting house rack for Hall C	PLC controllers' UPS
    Tyler Lemon 
    tlemon at jlab.org
       
    Thu Sep  6 09:36:58 EDT 2018
    
    
  
Hi Steve, 
I'll bring the cables to your office today. 
Also, I noticed an error in the drawing I attached in my last email. Jumpers in the connector drawing at the bottom did not match the manufacturer's drawing from the manual at the top. Attached is the corrected schematic for the cable. 
Tyler 
From: "Steve Lassiter" <lassiter at jlab.org> 
To: "Tyler Lemon" <tlemon at jlab.org> 
Sent: Thursday, September 6, 2018 9:05:18 AM 
Subject: Re: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Hi, 
Thanks , yes bring the cable by my office. 
Steven 
From: "Tyler Lemon" <tlemon at jlab.org> 
To: "Steve Lassiter" <lassiter at jlab.org> 
Cc: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Thursday, September 6, 2018 9:01:45 AM 
Subject: Re: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Hi Steve, 
We already have fabricated two ~30 ft long cables with 25-pin dsub connectors for the detector hut UPS units. I can drop them off today so they can be routed in the Hall. 
In the event 30 ft is not long enough, attached is the schematic and pin out for the connector. 
Best regards, 
Tyler 
From: "Steve Lassiter" <lassiter at jlab.org> 
To: "Tyler Lemon" <tlemon at jlab.org> 
Cc: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Thursday, September 6, 2018 8:49:08 AM 
Subject: Re: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Hello Tyler, 
Can you you provide me the schematic for the HMS and SHMS UPS 25 pin status cable? 
Thanks 
Steven 
From: "Tyler Lemon" <tlemon at jlab.org> 
To: "Steve Lassiter" <lassiter at jlab.org>, "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Tuesday, August 21, 2018 10:48:04 AM 
Subject: Re: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Hi Steve, 
Attached is a pdf of the UPS monitoring routines with color-coded comments on the different parts. 
Best regards, 
Tyler 
From: "Steve Lassiter" <lassiter at jlab.org> 
To: "Tyler Lemon" <tlemon at jlab.org> 
Sent: Friday, August 17, 2018 4:08:05 PM 
Subject: Re: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Send me the code mods in a pdf file. 
Steven 
From: "Tyler Lemon" <tlemon at jlab.org> 
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Friday, August 17, 2018 3:58:47 PM 
Subject: [Dsg-hallc_controls] Cable put in counting house rack for Hall C PLC controllers' UPS 
Hello Steve, 
This afternoon, Amanda, Pablo, and I put cables and terminal blocks in the rack with the PLC controllers' UPS on the second floor of the counting house. We put in the new terminal blocks to make it easier to add a second cable in the future if a hardwired signal to SHMS PLC is desired. This cabling setup will provide the 24 V signal indicating no fault with the UPS. 
Since you have suggested to leave the final wiring to Hall C technicians, there are two labeled cables with ends left free and taped. One cable needs to go to a 24 V power supply and the other needs to go to the PLC input channel. 
Attached is a photo of the rack and cables. The cable to the PLC is on the shelf above the PLC. The cable to the 24 V supply is on the floor. 
Also attached is a sketch of the wiring for the dsub-to-terminal-block adapter and cabling installed today. 
Once the input channels for each of the PLC are finalized, please let us know so we can update and give you the code to download to the PLC. 
Best regards, 
Tyler 
_______________________________________________ 
Dsg-hallc_controls mailing list 
Dsg-hallc_controls at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180906/9f5d07f2/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ferrups wiring and connector - UPDATED.jpg
Type: image/jpeg
Size: 50852 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180906/9f5d07f2/attachment-0001.jpg>
    
    
More information about the Dsg-hallc_controls