[Dsg-hallc_controls] UPS status
    Steve Lassiter 
    lassiter at jlab.org
       
    Tue Sep 11 16:48:48 EDT 2018
    
    
  
Hi, 
The status for the HMS_UPS does not appear to be working. A 24V dc source is from the rotation rack is being feed into pin 12 on the UPS and returned by pin 13 to the I/O module rotation:3 ch11.data. The ground of the 24VPSU is fed into the group3 common block of the I/O module. 
If the ferrups UPS uses a transistor with reference to its internal 12V psu, then an isolation relay will be need at the UPS connection, as the two dc psu will have different grounds. 
Steven 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180911/ef1c153b/attachment.html>
    
    
More information about the Dsg-hallc_controls
mailing list