[Dsg-hallc_controls] Quadrupole field regulation
Mike Fowler
fowler at jlab.org
Fri Sep 28 13:54:31 EDT 2018
Hi,
What is the sequence of inputs from the operator?
Mike
On 9/28/2018 1:30 PM, Amanda Hoebel wrote:
> Hi Mike,
>
> I have some questions/comments (in blue) on some of your comments for
> the current loop regulation.
>
> 4. If the analog signal I_coarse is less than the Last_I_Sent by even
> a small fraction the MOL value is used.
> Yes, as the PSU would be ramping up, even if it's by a small amount.
> This would only occur if someone were to set an I_target/Last_I_Sent
> value that was very close to what the power supply was already at. If
> that is not the correct method, what should be done instead?
>
> 7. Consider this:
> If I_coarse is equal to Last_I_Sent +/- a few amps
> true, MPS is at setpoint
> false, The MPS is still ramping, something happened, or the MPS
> tripped and the Last_I_Sent was not updated. (Interlock?)
> or the window is too small. Determine what to do.
> I am unsure of what you are suggesting. I will implement a condition
> where the loop stops if there is an interlock (as per comment #1) and
> can add a case where the program continues to the next rung if the
> PSU_Ready is True, in the event that the window is too small. Any
> other problem that could arise seems like it would be related to the
> PSU itself, not the program. The program does not ramp the PSU and
> stop ramp only if the current falls within the window. The PSU will
> stop at the set point given (no runaway condition possible).
>
> 8. Compare Q1_I_Target to Last_I_Sent to determine ramp direction
> instead of the analog I_coarse.
> Q1_I_Target and Last_I_Sent cannot be compared for ramp direction, as
> they will be the same value as each other on the ladder logic when the
> regulation routine is enabled.
>
> Regards,
> Amanda
>
> ------------------------------------------------------------------------
> *From: *"Amanda Hoebel" <amandah at jlab.org>
> *Sent: *Wednesday, September 26, 2018 10:04:46 AM
> *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
>
> ------------------------------------------------------------------------
> *From: *"Mike Fowler" <fowler at jlab.org>
> *To: *"dsg-hallc controls" <dsg-hallc_controls at jlab.org>
> *Sent: *Tuesday, September 25, 2018 10:37:25 AM
> *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
> Hi,
>
> Comments.
>
> The ability to manually input a current and send it without a MOL
> value has been removed.
> Must be included.
>
> Cheers,
> Mike
>
>
>
> On 9/20/2018 9:12 AM, Amanda Hoebel wrote:
>
> Hi Mike,
>
> I have attached pdfs of the field regulation routine for HMS Q1.
> If this is correct I will make the routines for HMS Q2 and Q3, and
> for the quads in SHMS.
>
> Regards,
> Amanda
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180928/184f2dfb/attachment.html>
More information about the Dsg-hallc_controls
mailing list