[Dsg-hallc_controls] Quadrupole field regulation

Mike Fowler fowler at jlab.org
Fri Sep 28 15:45:32 EDT 2018


 >>>the operator inputs an I_target value and then selects to start 
regulation, the I_target value will be stored as Last_I_sent

Perhaps I am missing the code where start regulation triggers where 
Last_I_Sent is made equal to I_target.

Mike





On 9/28/2018 3:02 PM, Amanda Hoebel wrote:
> If the operator inputs an I_target value and then selects to start 
> regulation, the I_target value will be stored as Last_I_sent (on the 
> function block diagram). On the ladder logic, I_coarse is basically 
> being compared to I_target, since I_target and Last_I_sent would be 
> the same value. The program would still work with the PSU starting 
> from zero.
>
>
> ------------------------------------------------------------------------
> *From: *"Mike Fowler" <fowler at jlab.org>
> *To: *"dsg-hallc controls" <dsg-hallc_controls at jlab.org>
> *Sent: *Friday, September 28, 2018 2:28:11 PM
> *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
> Condition one: PSU starting from zero
>
> Operator>  Inputs an I_target and I_MOL value.
> PLC> Checks I_target if in limits, sets the MPS_Wa_Value
> Operator> Start regulation
> PLC> Compares analog I_coarse to Last_I_Sent which is assumed to be zero.
>             If I_coarse > Last_I_Sent the code sends MPS_Wa_Value to 
> PSU.   Note: analog I_coarse value could be non zero and the MOL value 
> is not sent.
> PLC> Waits for I_coarse to be equal to MOL value +/-1%. Was the MOL 
> value ever sent?
>
> Mike
>
>
>
>
>
> On 9/28/2018 2:00 PM, Amanda Hoebel wrote:
>
>     The operator would input an I_target and I_MOL value, then select
>     to start regulation.
>
>
>     ------------------------------------------------------------------------
>     *From: *"Mike Fowler" <fowler at jlab.org>
>     *To: *"dsg-hallc controls" <dsg-hallc_controls at jlab.org>
>     *Sent: *Friday, September 28, 2018 1:54:31 PM
>     *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
>
>     Hi,
>
>     What is the sequence of inputs from the operator?
>
>     Mike
>
>
>
>     On 9/28/2018 1:30 PM, Amanda Hoebel wrote:
>
>         Hi Mike,
>
>         I have some questions/comments (in blue) on some of your
>         comments for the current loop regulation.
>
>         4. If the analog signal I_coarse is less than the Last_I_Sent
>         by even a small fraction the MOL value is used.
>         Yes, as the PSU would be ramping up, even if it's by a small
>         amount. This would only occur if someone were to set an
>         I_target/Last_I_Sent value that was very close to what the
>         power supply was already at. If that is not the correct
>         method, what should be done instead?
>
>         7. Consider this:
>         If I_coarse is equal to Last_I_Sent +/- a few amps
>             true, MPS is at setpoint
>             false, The MPS is still ramping, something happened, or
>         the MPS tripped and the Last_I_Sent was not updated. (Interlock?)
>                     or the window is too small. Determine what to do.
>         I am unsure of what you are suggesting. I will implement a
>         condition where the loop stops if there is an interlock (as
>         per comment #1) and can add a case where the program continues
>         to the next rung if the PSU_Ready is True, in the event that
>         the window is too small. Any other problem that could arise
>         seems like it would be related to the PSU itself, not the
>         program. The program does not ramp the PSU and stop ramp only
>         if the current falls within the window. The PSU will stop at
>         the set point given (no runaway condition possible).
>
>         8. Compare Q1_I_Target to Last_I_Sent to determine ramp
>         direction instead of the analog I_coarse.
>         Q1_I_Target and Last_I_Sent cannot be compared for ramp
>         direction, as they will be the same value as each other on the
>         ladder logic when the regulation routine is enabled.
>
>         Regards,
>         Amanda
>
>         ------------------------------------------------------------------------
>         *From: *"Amanda Hoebel" <amandah at jlab.org>
>         *Sent: *Wednesday, September 26, 2018 10:04:46 AM
>         *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
>
>         ------------------------------------------------------------------------
>         *From: *"Mike Fowler" <fowler at jlab.org>
>         *To: *"dsg-hallc controls" <dsg-hallc_controls at jlab.org>
>         *Sent: *Tuesday, September 25, 2018 10:37:25 AM
>         *Subject: *Re: [Dsg-hallc_controls] Quadrupole field regulation
>
>         Hi,
>
>         Comments.
>
>         The ability to manually input a current and send it without a
>         MOL value has been removed.
>         Must be included.
>
>         Cheers,
>         Mike
>
>
>
>         On 9/20/2018 9:12 AM, Amanda Hoebel wrote:
>
>             Hi Mike,
>
>             I have attached pdfs of the field regulation routine for
>             HMS Q1.  If this is correct I will make the routines for
>             HMS Q2 and Q3, and for the quads in SHMS.
>
>             Regards,
>             Amanda
>
>
>             _______________________________________________
>             Dsg-hallc_controls mailing list
>             Dsg-hallc_controls at jlab.org
>             https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
>         _______________________________________________
>         Dsg-hallc_controls mailing list
>         Dsg-hallc_controls at jlab.org
>         https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
>         _______________________________________________
>         Dsg-hallc_controls mailing list
>         Dsg-hallc_controls at jlab.org
>         https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
>     _______________________________________________
>     Dsg-hallc_controls mailing list
>     Dsg-hallc_controls at jlab.org
>     https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>     _______________________________________________
>     Dsg-hallc_controls mailing list
>     Dsg-hallc_controls at jlab.org
>     https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls