[Dsg-hallc_controls] Upgrading HMS controls
Tyler Lemon
tlemon at jlab.org
Mon Jan 14 16:50:58 EST 2019
Hello Steven,
To summarize what we talked about this afternoon, finished today, and the plan for tomorrow:
Today Amanda, Brian, and I updated the firmware on the HMS primary and redundant PLC from version 16.057 to version 20.058 and installed the new Ethernet (1756-EN2T), ControlNet (1756-CN2), and Redundancy (1756-RM2) modules received last summer in both the primary and secondary controller chassis.
To get the new redundancy modules working, we had to downgrade the firmware they came with to version 20.009. We were then able to get the HMS PLC program running and the redundancy modules synchronized. We saved the .ACD program file as "HMS_Controls_V21D.ACD" in M:\dsg-hallc_controls.
Right now, even though the system is up and running, there is a red LED blinking on the new redundancy modules indicating that only one fiber cable is connected. Since the PLC system is running fine, it does not seem like the second fiber cable is required to run. You mentioned that you would look into submitting a PR in for a second fiber cable to be able to clear the LED indicator on the modules.
Tomorrow, we will meet at 10:30AM in the counting house to test that the PLC system switches to the redundant chassis if the primary is disabled.
Best regards,
Tyler
________________________________
From: Dsg-hallc_controls <dsg-hallc_controls-bounces at jlab.org> on behalf of Amrit Yegneswaran <yeg at jlab.org>
Sent: Wednesday, January 9, 2019 10:53:23 AM
To: dsg-hallc controls
Cc: Patrizia Rossi
Subject: Re: [Dsg-hallc_controls] Upgrading HMS controls
hi steve,
for the upgrade on monday 01/14/2018 at 13:30, amanda, tyler, and brian will be present.
if the schedule changes, please post the new schedule, as you did this one, to this mailing list.
sincerely
amrit
________________________________
From: Dsg-hallc_controls <dsg-hallc_controls-bounces at jlab.org> on behalf of Steven Lassiter <lassiter at jlab.org>
Sent: Wednesday, January 9, 2019 9:23 AM
To: dsg-hallc controls
Subject: [Dsg-hallc_controls] Upgrading HMS controls
Hi,
Lets try to upgrade the software of the HMS PLC on Monday, weather permitting.
Say around 1:30pm meet in Hall C counting house?
Thanks
Steven
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20190114/1cb91750/attachment.html>
More information about the Dsg-hallc_controls