[Dsg-hallc_controls] Epics tags not updating

Brian Eng beng at jlab.org
Thu Jan 17 16:40:36 EST 2019


We found a setting that needs to be changed for the HMS PLC in the KEPServerEX 6 software that is being used to send the EPICS PVs to the PLC, unfortunately when we tried to change the value either it wouldn't take or the server wouldn't start back up after we thought we changed it.

Rebooting skylla7 took 20+ minutes and still didn't fix the problem.

We'll try downgrading (Steve found an article that suggests that might fix the problem) the controller firmware to 20.55 tomorrow since Mike is out on leave and might not be able to reply.

However, the long-term fix will be to run the latest firmware and either fix KEPServerEX or replace it with something else: An EPICS softIOC running on one of the existing Hall C servers along with archiving via Mya would be a much better supported solution for the future as multiple people would be able to work on it and/or it is supported site-wide, not even taking into account the costs.

> On Jan 17, 2019, at 2:40 PM, Steven Lassiter <lassiter at jlab.org> wrote:
> 
> I am back in the office.
> drop here and we can discuss
> thanks
> Steven
> From: Dsg-hallc_controls <dsg-hallc_controls-bounces at jlab.org> on behalf of Brian Eng <beng at jlab.org>
> Sent: Thursday, January 17, 2019 1:39:19 PM
> To: dsg-hallc controls
> Subject: Re: [Dsg-hallc_controls] Epics tags not updating
>  
> We tried looking for you in Hall C but didn't find you.
> 
> Will you be coming to the CH anytime soon?
> 
> I'd like to try and see if there's any options/settings in that software that need to be tweaked before reverting back to the old modules since CIP messaging definitely works okay with the new modules.
> 
> I tried logging in to skylla7, but someone was already logged in and didn't want to disconnect their session.




More information about the Dsg-hallc_controls mailing list