[Dsg-hallc_controls] [EXTERNAL] Re: CAEN-SY4527 test Results using Advanced GECO features

Pablo Campero Rojas campero at jlab.org
Tue Sep 10 09:48:59 EDT 2019


Hello Alberto,

Find my answers/comments in blue font bellow:


“(ERROR: Failed to register
../PABLO_SCRIPTS/HV-Board-36ch-hvcaentest2/All_HVBoards_Rup_36ch.js.) so
can you help us to solve this issue?”

To replicate the test with one board connected in the mainframe we do not need to run the HVCAEN-MainExpertControls.opi screen. The error is generated when a value is trying to be entered for the RUp parameter in that screen, and CS-Studio is not finding the associated script. I did not send those JavaScript that were developed to turn on/off or set six parameters for all 16 HV boards’ channels (576 channels) simultaneously. I can provide these eight JavaScripts, if you want to replicate the test with all 16 A7030TN boards connected.

Use the following CSS-BOY screens to replicate the tests:

     *   HVCAEN-7030TN-Expert_slot0.opi (controls/monitors turn on/off and main parameters for 36 channels)
     *   HVCAEN-7030TN-RampTest_slot0.opi (Monitor voltage ramp up/down for 36 channels)

Additionally, you must use the eight JavaScript (contained in the “slot0” folder) as part of the HVCAEN-7030TN-Expert_slot0 screen to control power on/off and six input parameters for all 36 channels simultaneously. Board has to be connected at slot 0.


“(one is a bug in the EPICS IOC the otheris a bug in the EPICS client)”.

It could be the EPICS client but keep in mind that a separate test by another user at JLab was performed  by using a different EPICS client /Program (NI-EPICS Client/cRIO) and found the similar issues with the addition of the random changes of the parameters for no reason. (Note: For that test, more than one A7030TN board was connected at the same time (x16)).


“We noticed also that the command order is different from EPCIS to GECO,
I mean using GECO the channels are powered averytime in the same order
(0,1,2,3, .., 35) while using EPICS the order is random, this lead me to
think that probably the EPCIS framework in same way desn't respect the
initial commands order. This behavior in principle it is not bad but due
to to the fact that the commands are not executed in milliseconds, there
cuold be little delay between a power-up of a channel and a power up of
the near channel.”

I already tried a 10, 100 and 1000 ms delay (in JavaScripts) between the power on/off and set parameters commands of each channel but it did not work. I noticed that most of the time I had randomly the missed channel/s turned on/off or with missed set parameters, as you noticed in the previous sent test results report.


 “I noted that you already send me some script but with different name,
are these the same as those requested by the .opi files and I only have
to rename them or need I something new?”

See first answer above. No need to re-name none of them, .opi files are already configure to read/run JavaScript that I sent.



Best Regards,

Pablo


________________________________
From: Alberto Lucchesi <a.lucchesi at caen.it>
Sent: Monday, September 9, 2019 12:23 PM
To: Pablo Campero Rojas <campero at jlab.org>; Greg Kibilko <greg at setechsales.com>; Gianni Di Maio <g.dimaio at caen.it>; Nicola Paoli <n.paoli at caen.it>; Enrico <e.pardini at caen.it>
Cc: dsg-hallc controls <dsg-hallc_controls at jlab.org>
Subject: [EXTERNAL] Re: CAEN-SY4527 test Results ussign Advanced GECO features

Dear Pablo,

I looked your report and the logfile you sent us.

Concernign the test 1, I noticed that the GECO logger did not record the
RUp/RDwn command so I presume the logger has been started after those
settings, this is bad because I did not see if all the ramp set commands
arrived to the mainframe (probably the channels with wrong ramp value
didn'r receive the set command).
The test shows that a couple of channels are not powered on/off and this
is confirmed by the log file , the power on/off command is not arrived
for the channels that showed issue.
There are two possible causes of this error (one is a bug in the EPICS
IOC the otheris a bug in the EPICS client).
We are now trying to replicate the issue, we fought a little with cs
studio because we never used it, but now we are near to be able to use
it, now we are having an error because some script ar enot present
(ERROR: Failed to register
../PABLO_SCRIPTS/HV-Board-36ch-hvcaentest2/All_HVBoards_Rup_36ch.js.) so
can you help us to solve this issue?
As soon as we are able to run the test we can see where the command are
missed because we can start the IOC in DEBUG mode and see its I/O.

Concerning the test2 we noticed that using GECO all the commands are
received by the SY4527 and this confirm the fact that the issue is
related to the couple EPICS IOC/client.
We noticed also that the command order is different from EPCIS to GECO,
I mean using GECO the channels are powered averytime in the same order
(0,1,2,3, .., 35) while using EPICS the order is random, this lead me to
think that probably the EPCIS framework in same way desn't respect the
initial commands order. This behavior in principle it is not bad but due
to to the fact that the commands are not executed in milliseconds, there
cuold be little delay between a power-up of a channel and a power up of
the near channel.

In test 2 there is a channel that for two times had a delay of the ramp,
it is not the channel 17 (as described in the document) but it is the
channel 23. We don't have an explanation about this wrong behavior, we
never experienced something like that and we woudl like to reproduce
here the issue with one of our board using your EPICS software (we are
trying).

The fact that GECO and ssh showed the same result while EPICS client has
different values) confirm that the system is correctly working and the
issue is related to the EPICS IOC/Client. As soon as we are able to run
the CSS test we hope to give you more details about this wrong behavior.

I think the right steps are:
- understand better the problem showed in your test (we are doing it)
- fix it
- increase the complexity of the setup and see the result.


I noted that you already send me some script but with different name,
are these the same as those requested by the .opi files and I only have
to rename them or need I something new?

Best Regards,

Alberto
Il 06/09/2019 15:39, Pablo Campero Rojas ha scritto:
> Hello Gianni and Greg,
>
> Attached find report for the tests performed for CAEN A7030 HV board, the report shows the results for two test:
>
> Test 1: Tested CAEN A7030 HV board by setting and monitoring PVs using CSS-BOY screens with Advanced Logging Feature enabled.
> Test 2:  Tested CAEN A7030 HV board using GECO2020 Script and logging Advanced Features.
>
> The data log files and additional screenshots for each test can be found at: https://userweb.jlab.org/~campero/
>
> Let me know if you have any issues to access to the files.
>
> Best Regards,
> Pablo Campero
>
>
> ________________________________
> From: Greg Kibilko <greg at setechsales.com>
> Sent: Wednesday, September 4, 2019 8:51 AM
> To: Pablo Campero Rojas <campero at jlab.org>
> Subject: Re: Re-sending email with link to download files requested
>
> Hi Pablo,
>
> Just a quick note to check your status.  Have you had a chance to perform the tests requested by CAEN?
>
> Cheers,
> Greg
>
> On 8/28/2019 11:25 AM, Pablo Campero Rojas wrote:
> Hello Gianni,
>
> Thank you for the code and the instructions. I'll be performing this test in the upcoming days and I'll get back to you once I have the results.
>
> Best Regards,
> Pablo
>
>
> ________________________________
> From: Gianni Di Maio <g.dimaio at caen.it><mailto:g.dimaio at caen.it>
> Sent: Wednesday, August 28, 2019 10:36 AM
> To: Pablo Campero Rojas <campero at jlab.org><mailto:campero at jlab.org>
> Cc: Alberto Lucchesi <a.lucchesi at caen.it><mailto:a.lucchesi at caen.it>; Nicola Paoli <n.paoli at caen.it><mailto:n.paoli at caen.it>; Enrico <e.pardini at caen.it><mailto:e.pardini at caen.it>; Greg Kibilko <greg at setechsales.com><mailto:greg at setechsales.com>
> Subject: Re: Re-sending email with link to download files requested
>
> Hello Pablo,
>
> here is the code to activate the logging function.
>
> d14146h04187f00221m03
>
> Concerning  the instructions to activate the functionality are available in the user manual attached.
> SYx527 System Advanced Features at page 27.
>
> Very good to know that you see the problem even with the GECO alone, but, for our test please use both( ie GECO + EPICS software)
> Once you have connected GECO please enable immediately the log for all the parameters of the board you are testing ( start with only one board for the moment).
> Use your EPICS software to do the test and once reproduced the problem stop the GECO logging and send us the entire logfile describing us what happened.
> At the moment we do not have an A7030 board available so right now we can not do the same test, but we will soon.
>
> Best regards.
> Gianni
>
> Il 28/08/2019 00:50, Gianni Di Maio ha scritto:
> Hello Pablo,
> message received...
> Tomorrow I will try to download the files.
> OK proceed with the test with A7030 board.
> Tomorrow I will let you know the activation code and relative instructions.
> Best regards.
> Gianni
>
> Il 27/08/2019 20:31, Pablo Campero Rojas ha scritto:
> Hello Gianni,
>
> I sent you the email below a few hours ago, but it seems like caen.it has rejected the email, I got a "security/policy settings issues at caen.it".
>
> I'm assuming that the issues are the result of the attempts to send you a .zip file, which had all the EPICS files that I used for my test.
> Please try these link instead:  https://userweb.jlab.org/~campero/
> Let me know if you can get the files this time.
>
>
>                                                                                                                                                                                                                                                                       .
> Hello Gianni,
>
> To clarify or add one point more to the summary that you mentioned; the arbitrarily changes from its pre-set values issue also has been noticed while a user at JLab was using only GECO2020 with no external EPICS client as part of the test setup.
>
>
> Currently, DSG group does not have on hand the  A7435 HV board to get the recommended setup; we do have HV board A7030 that we could use instead. Is that ok for the recommended test?
>
> The serial number for the SY4528 Basic CPU: 0760.
> Please send me details instructions to activate this functionality/option in GECO2020, which will help to solve the issues.
>
>
> Attached is a zip file with the EPIS CSS-BOY screens (.opi files) and Java scripts (.js files that run as part of the CSS screens) used to test SY4527 systems.
> The specifications about the setup and details for the software versions used for the test can be find at: https://www.jlab.org/div_dept/physics_division/dsg/presentations2/Hall%20C%20HV%20CAEN%20Test%20Results.pdf
>
> Best Regards,
>
> Pablo Campero
> Detector Support Group
> Jefferson Lab
> 757-269-7034
>
>
>
>
>
> --
>   CAEN S.p.A.   Gianni Di Maio
> Maintenance Division Manager
> Email: g.dimaio at caen.it<mailto:g.dimaio at caen.it>
> Skype: gdimaio_caen
> Cell:+393482556525
>
> CAEN S.p.A.
> Tel.: +39 0584 388 398
> Fax: +39 0584 388 959
> Email: info at caen.it<mailto:info at caen.it>
> via Vetraia,11 • 55049 • Viareggio (LU) • Italy
> Cod.Fisc. e p.IVA IT00864500467
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwIF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=C9l7VLVY2CjU9VF3rf_9p8Ob5VnJ_uJtMCx_CJovZdg&s=1YcsNaBfDXCLlmV4aSpWjvpIlvwL3ggiZDSRN0JTuf8&e= <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=E-P8t1rpOcX8LElZZhOE0mKQI61LJDakqpB08crZI18&s=2fsoHSr_K9zdQEP7A3baz0OQ4gcl3HP5P_T0n9X02o4&e=>
>
> Le informazioni trasmesse attraverso la presente comunicazione via mail ed eventuali allegati sono da intendersi di esclusiva spettanza del destinatario. Nel caso in cui le stesse raggiungessero, per qualunque motivo, soggetti diversi dai destinatari, questi dovrebbero darne immediata notizia al mittente. In ogni caso, eventuali soggetti diversi dai legittimi destinatari della presente comunicazione sono esplicitamente diffidati da ogni utilizzazione, sia ai sensi del D.Lgs. n. 196/2003 "Codice in materia di protezione dei dati personali" sia ai sensi degli art. 616 e ss. Codice Penale che sanziona la violazione del segreto sulla corrispondenza.
> The information contained in this transmission may contain privileged and confidential information and is intended only for the use of the person(s)named above. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, any review, dissemination, distribution or duplication of this communication is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and destroy all copies of the original message.
>
> --
>   CAEN S.p.A.   Gianni Di Maio
> Maintenance Division Manager
> Email: g.dimaio at caen.it<mailto:g.dimaio at caen.it>
> Skype: gdimaio_caen
> Cell:+393482556525
>
> CAEN S.p.A.
> Tel.: +39 0584 388 398
> Fax: +39 0584 388 959
> Email: info at caen.it<mailto:info at caen.it>
> via Vetraia,11 • 55049 • Viareggio (LU) • Italy
> Cod.Fisc. e p.IVA IT00864500467
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwIF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=C9l7VLVY2CjU9VF3rf_9p8Ob5VnJ_uJtMCx_CJovZdg&s=1YcsNaBfDXCLlmV4aSpWjvpIlvwL3ggiZDSRN0JTuf8&e= <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=E-P8t1rpOcX8LElZZhOE0mKQI61LJDakqpB08crZI18&s=2fsoHSr_K9zdQEP7A3baz0OQ4gcl3HP5P_T0n9X02o4&e=>
>
> Le informazioni trasmesse attraverso la presente comunicazione via mail ed eventuali allegati sono da intendersi di esclusiva spettanza del destinatario. Nel caso in cui le stesse raggiungessero, per qualunque motivo, soggetti diversi dai destinatari, questi dovrebbero darne immediata notizia al mittente. In ogni caso, eventuali soggetti diversi dai legittimi destinatari della presente comunicazione sono esplicitamente diffidati da ogni utilizzazione, sia ai sensi del D.Lgs. n. 196/2003 "Codice in materia di protezione dei dati personali" sia ai sensi degli art. 616 e ss. Codice Penale che sanziona la violazione del segreto sulla corrispondenza.
> The information contained in this transmission may contain privileged and confidential information and is intended only for the use of the person(s)named above. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, any review, dissemination, distribution or duplication of this communication is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and destroy all copies of the original message.
>
> --
> Greg Kibilko
> SETS - SE Technical Sales, Inc.
> 112 Tyra Lane
> Townville, SC 29689
> P: (864) 356-2606
> CAEN Products<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it_csite&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=EKYIDEH5c_qBONS0ZtpytsfH21iBGjnfDemmcBZ97wc&s=1eeoi4jZPyvQnEEf2hyhlGsCpr4_cfwb9kVnS0gB6zA&e=>
> CAEN SyS Products & Solutions<https://urldefense.proofpoint.com/v2/url?u=https-3A__caensys.com_products-2Dand-2Dsolutions_&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=EKYIDEH5c_qBONS0ZtpytsfH21iBGjnfDemmcBZ97wc&s=Q-WOOcM3qQOAaPYtd-li08YCoG4tlCcBw_F9xedkU-Y&e=>
> IOxOs Products<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ioxos.ch&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=LBO4X3ekFDih7d6NqFyLjA&m=EKYIDEH5c_qBONS0ZtpytsfH21iBGjnfDemmcBZ97wc&s=0ubwG8gKZKsSe_dxMOR92YxzmPuEZ-KHQ0954wsHvq0&e=>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20190910/caf56147/attachment-0001.html>


More information about the Dsg-hallc_controls mailing list