Hi Aaron,
I'm curious if you've seen any correlation between the disconnects and 
the problems with the boards that have the SL pin pushing out?  Could 
there be a connection?
Best,
Greg
On 2/24/2020 11:38 AM, Aaron Brown wrote:
> Hello Alberto,
>
> This is wonderful news!
> I look forward to receiving the new HiVocs version soon.
>
> Best Regards,
> Aaron Brown
> ------------------------------------------------------------------------
> *From:* Alberto Lucchesi <a.lucchesi at caen.it>
> *Sent:* Monday, February 24, 2020 10:22 AM
> *To:* Aaron Brown <ambrown at jlab.org>; Gianni Di Maio 
> <g.dimaio at caen.it>; Greg Kibilko <greg at setechsales.com>; Amrit 
> Yegneswaran <yeg at jlab.org>
> *Cc:* Patrizia Rossi <rossi at jlab.org>; dsg-hallc controls 
> <dsg-hallc_controls at jlab.org>
> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector Pin 
> Question
> Hi Aaron,
>
> I'was able to reproduce the random parameter changes issue.
>
> The issue was not visible with only one board because it is related to 
> the parallelism inside the IOC.
>
> What was happening is that with several boards the EPICS framework 
> (our IOC is based over it) calls parts of our code in parallel and 
> there was an internal structure that was not thread-safe. The results 
> were that some settings were not applied to the right parameter but to 
> onother one (the aren't random parameter changes, The values were 
> right but the parameters were wrong! (i.e., a Trip = 40 were codified 
> as VSet = 40 or a PW = On where codified as RUp = 1).
>
> I fixed the issue and now I'm testing the results and the issues seem 
> to be resolved. I'll do other tests in these days then I'll send you a 
> new HiVocs version within a couple of days.
>
> I don't have news about the other issue (the board disconnection) in 
> all my test I never experienced a board disconnection.
>
>
> Best Regards,
> Albert
>
>
> Il 24/02/2020 14:14, Aaron Brown ha scritto:
>> Hello Gianni,
>>
>> Yes, April works for us. We will have all the boards in our 
>> possession on hand for any rework that can be done.
>>
>> Best regards,
>> Aaron Brown
>> ------------------------------------------------------------------------
>> *From:* Gianni Di Maio <g.dimaio at caen.it> <mailto:g.dimaio at caen.it>
>> *Sent:* Friday, February 21, 2020 5:13 PM
>> *To:* Greg Kibilko <greg at setechsales.com> 
>> <mailto:greg at setechsales.com>; Aaron Brown <ambrown at jlab.org> 
>> <mailto:ambrown at jlab.org>; Amrit Yegneswaran <yeg at jlab.org> 
>> <mailto:yeg at jlab.org>
>> *Cc:* Patrizia Rossi <rossi at jlab.org> <mailto:rossi at jlab.org>; 
>> dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>> <mailto:dsg-hallc_controls at jlab.org>; Alberto Lucchesi 
>> <a.lucchesi at caen.it> <mailto:a.lucchesi at caen.it>
>> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector Pin 
>> Question
>> Dear Aaron,
>>
>> as told by Greg April could be OK with us to visit you.
>> If possible I would like to have a look to all the boards connectors 
>> ( to rework partially the RADIALL connector and in particularly the 
>> safety loop pin).
>> Anyway for the moment just let me know if April is OK,  I will send 
>> later a list of rework I would like to do on the boards and cables.
>>
>> Have a nice week end to everybody
>> Gianni
>> Il 18/02/2020 21:03, Greg Kibilko ha scritto:
>>> Hi Aaron,
>>>
>>> Very good.  Gianni is home sick, but I did Skype with him and his 
>>> schedule for March is full.  We're aiming for April.  I should be 
>>> able to propose some dates for you this week.
>>>
>>> Best,
>>> Greg
>>>
>>> On 2/18/2020 1:31 PM, Aaron Brown wrote:
>>>> Hi Greg,
>>>>
>>>> If April is the best time for you guys, it works for us.
>>>>
>>>> Best regards,
>>>> Aaron
>>>> ------------------------------------------------------------------------
>>>> *From:* Greg Kibilko <greg at setechsales.com> 
>>>> <mailto:greg at setechsales.com>
>>>> *Sent:* Tuesday, February 18, 2020 10:38 AM
>>>> *To:* Aaron Brown <ambrown at jlab.org> <mailto:ambrown at jlab.org>; 
>>>> Gianni Di Maio <g.dimaio at caen.it> <mailto:g.dimaio at caen.it>; Amrit 
>>>> Yegneswaran <yeg at jlab.org> <mailto:yeg at jlab.org>
>>>> *Cc:* Patrizia Rossi <rossi at jlab.org> <mailto:rossi at jlab.org>; 
>>>> dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>>>> <mailto:dsg-hallc_controls at jlab.org>; Alberto Lucchesi 
>>>> <a.lucchesi at caen.it> <mailto:a.lucchesi at caen.it>
>>>> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector Pin 
>>>> Question
>>>> Hi Aaron,
>>>>
>>>> Ok, fantastic.  This gives us plenty of time to work with.
>>>>
>>>> How about timeline?  Is April too late?
>>>>
>>>> Cheers,
>>>> Greg
>>>>
>>>> On 2/18/2020 10:36 AM, Aaron Brown wrote:
>>>>> Morning Greg,
>>>>>
>>>>> The only day/time I can think of that /might/ pose a problem would 
>>>>> be Wednesday afternoons between 1 and 3.
>>>>> Other than that, there is nothing that can't be worked around.
>>>>>
>>>>> Thanks,
>>>>> Aaron
>>>>> ------------------------------------------------------------------------
>>>>> *From:* Greg Kibilko <greg at setechsales.com> 
>>>>> <mailto:greg at setechsales.com>
>>>>> *Sent:* Tuesday, February 18, 2020 10:32 AM
>>>>> *To:* Aaron Brown <ambrown at jlab.org> <mailto:ambrown at jlab.org>; 
>>>>> Gianni Di Maio <g.dimaio at caen.it> <mailto:g.dimaio at caen.it>; Amrit 
>>>>> Yegneswaran <yeg at jlab.org> <mailto:yeg at jlab.org>
>>>>> *Cc:* Patrizia Rossi <rossi at jlab.org> <mailto:rossi at jlab.org>; 
>>>>> dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>>>>> <mailto:dsg-hallc_controls at jlab.org>; Alberto Lucchesi 
>>>>> <a.lucchesi at caen.it> <mailto:a.lucchesi at caen.it>
>>>>> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector Pin 
>>>>> Question
>>>>> Hi Aaron,
>>>>>
>>>>> I am sure Gianni will agree that a visit is in order.
>>>>>
>>>>> In the next couple of months are there any specific days/weeks we 
>>>>> should target to visit? Or days/weeks we should try to avoid?
>>>>>
>>>>> Thanks!
>>>>> Greg
>>>>>
>>>>> On 2/18/2020 10:30 AM, Aaron Brown wrote:
>>>>>> Hello Gianni,
>>>>>>
>>>>>> We currently have 33 A7030TN modules and 2 SY4527 crates on hand.
>>>>>> I think that best idea would be to have someone from CAEN make a 
>>>>>> visit to the lab and take a look/fix the connector pins.
>>>>>>
>>>>>> Best regards,
>>>>>> Aaron Brown
>>>>>> ------------------------------------------------------------------------
>>>>>> *From:* Gianni Di Maio <g.dimaio at caen.it> <mailto:g.dimaio at caen.it>
>>>>>> *Sent:* Monday, February 17, 2020 12:12 PM
>>>>>> *To:* Aaron Brown <ambrown at jlab.org> <mailto:ambrown at jlab.org>; 
>>>>>> Amrit Yegneswaran <yeg at jlab.org> <mailto:yeg at jlab.org>
>>>>>> *Cc:* Patrizia Rossi <rossi at jlab.org> <mailto:rossi at jlab.org>; 
>>>>>> dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>>>>>> <mailto:dsg-hallc_controls at jlab.org>; Greg Kibilko 
>>>>>> <greg at setechsales.com> <mailto:greg at setechsales.com>; Alberto 
>>>>>> Lucchesi <a.lucchesi at caen.it> <mailto:a.lucchesi at caen.it>
>>>>>> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector Pin 
>>>>>> Question
>>>>>> Hello Aaron,
>>>>>> thank you very much for the details.
>>>>>> Really strange a so high number of problems on the panel 
>>>>>> connector, as told from our experience it is more problematic the 
>>>>>> cable connector, this is the reason that we add the hot glue.
>>>>>> At this point let me know how you wish proceed.
>>>>>> To rework/repair the boards with pins pushed out we have two 
>>>>>> solutions, you ship the boards to our office in NY, or I could 
>>>>>> make an intervention in JLAB in spring.
>>>>>> How many boards you have in total?
>>>>>> May be it's worth to have a look to al the boards.
>>>>>>
>>>>>> Waiting your comments.
>>>>>> Best regards.
>>>>>> Gianni
>>>>>>
>>>>>> Il 14/02/2020 16:48, Aaron Brown ha scritto:
>>>>>>> Hello Gianni,
>>>>>>>
>>>>>>> We have experienced the issue of pins getting pushed back 12 
>>>>>>> separate times;
>>>>>>> 8 times it was the pins for the safety loops, and 4 times is was 
>>>>>>> an arbitrary pin.
>>>>>>> All occurrences were on the board R52 connector (male).
>>>>>>> I have attached a photo to highlight exactly what we're describing.
>>>>>>> Also attached is a photo of the inside of one of the boards 
>>>>>>> showing how the channel pins
>>>>>>> are strain relieved, but the safety loop pins are not.
>>>>>>>
>>>>>>> If you have any questions, please do not hesitate to send an 
>>>>>>> email to the mailing list.
>>>>>>>
>>>>>>> Warm regards,
>>>>>>> Aaron Brown
>>>>>>> ------------------------------------------------------------------------
>>>>>>> *From:* Dsg-hallc_controls <dsg-hallc_controls-bounces at jlab.org> 
>>>>>>> <mailto:dsg-hallc_controls-bounces at jlab.org> on behalf of Gianni 
>>>>>>> Di Maio <g.dimaio at caen.it> <mailto:g.dimaio at caen.it>
>>>>>>> *Sent:* Friday, February 14, 2020 3:26 AM
>>>>>>> *To:* Amrit Yegneswaran <yeg at jlab.org> <mailto:yeg at jlab.org>
>>>>>>> *Cc:* Patrizia Rossi <rossi at jlab.org> <mailto:rossi at jlab.org>; 
>>>>>>> dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>>>>>>> <mailto:dsg-hallc_controls at jlab.org>; Greg Kibilko 
>>>>>>> <greg at setechsales.com> <mailto:greg at setechsales.com>; Alberto 
>>>>>>> Lucchesi <a.lucchesi at caen.it> <mailto:a.lucchesi at caen.it>
>>>>>>> *Subject:* Re: [Dsg-hallc_controls] [EXTERNAL] CAEN Connector 
>>>>>>> Pin Question
>>>>>>> Dear Amrit,
>>>>>>>
>>>>>>> thank you for your email, I apologize I was not aware about the 
>>>>>>> dsg mailing list (dsg-hallc_controls at jlab.org 
>>>>>>> <mailto:dsg-hallc_controls at jlab.org>).
>>>>>>> I full agree with you the pushed pins issue will be surely 
>>>>>>> addressed by CAEN, we are considering to do a maintenance 
>>>>>>> intervention at JLAB in the next future.
>>>>>>> What I would like to know  to have a clear idea of the situation is
>>>>>>> How many boards with pushed pin/s you have?
>>>>>>> How many pins per board?
>>>>>>> If I well understood ( but may be I'm wrong) there are 4 boards 
>>>>>>> with this issue, that is one pin pushed back,and every time is 
>>>>>>> one of the two safety pin loop.
>>>>>>>
>>>>>>> Could you or some one of the group confirm me these numbers?
>>>>>>>
>>>>>>> Or in case I'm wrong could you provide me a report updated to today?
>>>>>>>
>>>>>>>
>>>>>>> Best regards.
>>>>>>>
>>>>>>> Gianni
>>>>>>>
>>>>>>>
>>>>>>> Il 13/02/2020 19:16, Amrit Yegneswaran ha scritto:
>>>>>>>> hello,
>>>>>>>> this issue of pushed pins needs to be addressed by CAEN.
>>>>>>>> dsg is not in this business.
>>>>>>>> also, i am very disappointed that i'm receiving the gianni's 
>>>>>>>> e-mail only today now.
>>>>>>>> i urge all of you, for the sake of transparency,  particularly 
>>>>>>>> from the caen side to use the mailing list, like we do here at 
>>>>>>>> jlab.
>>>>>>>> amrit
>>>>>>>> if anyone in the dsg group receives a "singular" e-mail make 
>>>>>>>> sure you broadcast it to the mailing list.
>>>>>>>> ------------------------------------------------------------------------
>>>>>>>> *From:* Dsg-hallc_controls 
>>>>>>>> <dsg-hallc_controls-bounces at jlab.org> 
>>>>>>>> <mailto:dsg-hallc_controls-bounces at jlab.org> on behalf of Brian 
>>>>>>>> Eng <beng at jlab.org> <mailto:beng at jlab.org>
>>>>>>>> *Sent:* Thursday, February 13, 2020 12:32 PM
>>>>>>>> *To:* dsg-hallc controls <dsg-hallc_controls at jlab.org> 
>>>>>>>> <mailto:dsg-hallc_controls at jlab.org>
>>>>>>>> *Subject:* [Dsg-hallc_controls] Fwd: [EXTERNAL] CAEN Connector 
>>>>>>>> Pin Question
>>>>>>>> In regards to Brad's previous email about the potting material 
>>>>>>>> here's one of the emails CAEN sent.
>>>>>>>>
>>>>>>>> Still waiting on more feedback since we've definitely seen it 
>>>>>>>> on the board side multiple times.
>>>>>>>>
>>>>>>>>> Begin forwarded message:
>>>>>>>>>
>>>>>>>>> *From: *Gianni Di Maio <g.dimaio at caen.it 
>>>>>>>>> <mailto:g.dimaio at caen.it>>
>>>>>>>>> *Subject: **Re: [EXTERNAL] CAEN Connector Pin Question*
>>>>>>>>> *Date: *February 6, 2020 at 5:42:31 PM EST
>>>>>>>>> *To: *Brian Eng <beng at jlab.org <mailto:beng at jlab.org>>
>>>>>>>>> *Cc: *Greg Kibilko <greg at setechsales.com 
>>>>>>>>> <mailto:greg at setechsales.com>>
>>>>>>>>>
>>>>>>>>> Dear Brian,
>>>>>>>>>
>>>>>>>>> please could you tell me if the pins pushed out are present 
>>>>>>>>> only on the RADIALL connector installed on the boards 
>>>>>>>>> (female)  or even on the RADIALL connectors installed on the 
>>>>>>>>> cables ( male).
>>>>>>>>> >From my experience usually in the past the problem appeared 
>>>>>>>>> only on cable side, this is the reason that we decided to add 
>>>>>>>>> the hot glue, in order to strengthen the tightness of the pin 
>>>>>>>>> and prevent a possible escape from the correct position, but 
>>>>>>>>> this as said only for the cable connector.
>>>>>>>>> The problem on the panel connector is very rare, how many 
>>>>>>>>> problematic boards you have  with pins pushed out?
>>>>>>>>> Could you send me some pictures?
>>>>>>>>>
>>>>>>>>> Best regards.
>>>>>>>>> Gianni
>>>>>>>>
>>>>>>>
>>>>>>> -- 
>>>>>>>
>>>>>>>  CAEN S.p.A.  Gianni Di Maio
>>>>>>>
>>>>>>> *Maintenance Division Manager*
>>>>>>>
>>>>>>> Email: g.dimaio at caen.it <mailto:g.dimaio at caen.it>
>>>>>>>
>>>>>>> Skype: gdimaio_caen
>>>>>>>
>>>>>>> 	Cell:+393482556525 	
>>>>>>>
>>>>>>> *CAEN S.p.A.*
>>>>>>>
>>>>>>> Tel.: +39 0584 388 398
>>>>>>> Fax: +39 0584 388 959
>>>>>>> Email: info at caen.it <mailto:info at caen.it>
>>>>>>> via Vetraia,11 • 55049 • Viareggio (LU) • Italy
>>>>>>> Cod.Fisc. e p.IVA IT00864500467
>>>>>>> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=xYez4K2x9z15rmeiciSi7NPPqL4bhatIr-SD73KGw8c&e=  
>>>>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=NkBWvHI5Zs-9oXlFaDnzpnLIvyQVuV_qo4jAGvl6JM8&s=HXuJxESZtIm45hzrZH6q0YrYEYtV0J5kDumRkl8BGW4&e=> 
>>>>>>>
>>>>>>>
>>>>>>> Le informazioni trasmesse attraverso la presente comunicazione 
>>>>>>> via mail ed eventuali allegati sono da intendersi di esclusiva 
>>>>>>> spettanza del destinatario. Nel caso in cui le stesse 
>>>>>>> raggiungessero, per qualunque motivo, soggetti diversi dai 
>>>>>>> destinatari, questi dovrebbero darne immediata notizia al 
>>>>>>> mittente. In ogni caso, eventuali soggetti diversi dai legittimi 
>>>>>>> destinatari della presente comunicazione sono esplicitamente 
>>>>>>> diffidati da ogni utilizzazione, sia ai sensi del D.Lgs. n. 
>>>>>>> 196/2003 "Codice in materia di protezione dei dati personali" 
>>>>>>> sia ai sensi degli art. 616 e ss. Codice Penale che sanziona la 
>>>>>>> violazione del segreto sulla corrispondenza.
>>>>>>> The information contained in this transmission may contain 
>>>>>>> privileged and confidential information and is intended only for 
>>>>>>> the use of the person(s)named above. If you are not the intended 
>>>>>>> recipient, or an employee or agent responsible for delivering 
>>>>>>> this message to the intended recipient, any review, 
>>>>>>> dissemination, distribution or duplication of this communication 
>>>>>>> is strictly prohibited. If you are not the intended recipient, 
>>>>>>> please contact the sender immediately and destroy all copies of 
>>>>>>> the original message.
>>>>>>>
>>>>>>
>>>>>> -- 
>>>>>>
>>>>>>  CAEN S.p.A.  Gianni Di Maio
>>>>>>
>>>>>> *Maintenance Division Manager*
>>>>>>
>>>>>> Email: g.dimaio at caen.it <mailto:g.dimaio at caen.it>
>>>>>>
>>>>>> Skype: gdimaio_caen
>>>>>>
>>>>>> 	Cell:+393482556525 	
>>>>>>
>>>>>> *CAEN S.p.A.*
>>>>>>
>>>>>> Tel.: +39 0584 388 398
>>>>>> Fax: +39 0584 388 959
>>>>>> Email: info at caen.it <mailto:info at caen.it>
>>>>>> via Vetraia,11 • 55049 • Viareggio (LU) • Italy
>>>>>> Cod.Fisc. e p.IVA IT00864500467
>>>>>> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=xYez4K2x9z15rmeiciSi7NPPqL4bhatIr-SD73KGw8c&e=  
>>>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=CK4IA3vcXcfmGx6m3v3SLbVbALDNmIRVqwR42dIp0vQ&s=3g8vV8eb0W81I5E9dK0wOFl7hjtwyjGD3KSLHzdqEd4&e=> 
>>>>>>
>>>>>>
>>>>>> Le informazioni trasmesse attraverso la presente comunicazione 
>>>>>> via mail ed eventuali allegati sono da intendersi di esclusiva 
>>>>>> spettanza del destinatario. Nel caso in cui le stesse 
>>>>>> raggiungessero, per qualunque motivo, soggetti diversi dai 
>>>>>> destinatari, questi dovrebbero darne immediata notizia al 
>>>>>> mittente. In ogni caso, eventuali soggetti diversi dai legittimi 
>>>>>> destinatari della presente comunicazione sono esplicitamente 
>>>>>> diffidati da ogni utilizzazione, sia ai sensi del D.Lgs. n. 
>>>>>> 196/2003 "Codice in materia di protezione dei dati personali" sia 
>>>>>> ai sensi degli art. 616 e ss. Codice Penale che sanziona la 
>>>>>> violazione del segreto sulla corrispondenza.
>>>>>> The information contained in this transmission may contain 
>>>>>> privileged and confidential information and is intended only for 
>>>>>> the use of the person(s)named above. If you are not the intended 
>>>>>> recipient, or an employee or agent responsible for delivering 
>>>>>> this message to the intended recipient, any review, 
>>>>>> dissemination, distribution or duplication of this communication 
>>>>>> is strictly prohibited. If you are not the intended recipient, 
>>>>>> please contact the sender immediately and destroy all copies of 
>>>>>> the original message.
>>>>>>
>>>>>
>>>>> -- 
>>>>> *Greg Kibilko*
>>>>> *SETS - SE Technical Sales, Inc.*
>>>>> 112 Tyra Lane
>>>>> Townville, SC 29689
>>>>> P: (864) 356-2606
>>>>> CAEN Products 
>>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it_csite&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=Ny4G7qu4sv_T0NtiToDEcRuwjKB8XwFEyYHHIK3W5Sg&s=3nJ2zMdxx2iYrQfVevkoQ136crvz5WPX-u9vLXbDKyc&e=>
>>>>> CAEN SyS Products & Solutions 
>>>>> <https://urldefense.proofpoint.com/v2/url?u=https-3A__caensys.com_products-2Dand-2Dsolutions_&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=Ny4G7qu4sv_T0NtiToDEcRuwjKB8XwFEyYHHIK3W5Sg&s=skGqBl6x9y3h92KiLpckUYhVQAtLyVD90zuz4wljKO4&e=>
>>>>> IOxOs Products 
>>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ioxos.ch&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=Ny4G7qu4sv_T0NtiToDEcRuwjKB8XwFEyYHHIK3W5Sg&s=OLAIrxGqeN6aRvKctgEs_ax0G-qYK9hWu6Do-hdBywM&e=>
>>>>
>>>> -- 
>>>> *Greg Kibilko*
>>>> *SETS - SE Technical Sales, Inc.*
>>>> 112 Tyra Lane
>>>> Townville, SC 29689
>>>> P: (864) 356-2606
>>>> CAEN Products 
>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it_csite&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=RuKyQ246VCfLgDisBhNfXaVwXLPxS8snA1X68m1DNYk&s=OnPfX_7lx0ht8FdYXuDrd7OFUQ58Ifa1FEn5qe97ndk&e=>
>>>> CAEN SyS Products & Solutions 
>>>> <https://urldefense.proofpoint.com/v2/url?u=https-3A__caensys.com_products-2Dand-2Dsolutions_&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=RuKyQ246VCfLgDisBhNfXaVwXLPxS8snA1X68m1DNYk&s=LjH-sZKE_oLptW3aG24eGtFrP1pCGT8A5-PZU5mC3xI&e=>
>>>> IOxOs Products 
>>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ioxos.ch&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=RuKyQ246VCfLgDisBhNfXaVwXLPxS8snA1X68m1DNYk&s=cxNHULDWIflLFm2_PSTqcGcmRiirjlGJyPqqHNTYsB8&e=>
>>>
>>> -- 
>>> *Greg Kibilko*
>>> *SETS - SE Technical Sales, Inc.*
>>> 112 Tyra Lane
>>> Townville, SC 29689
>>> P: (864) 356-2606
>>> CAEN Products 
>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it_csite&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=ksMkvqymFO1sFCHsTbtFDMSRRxzdO2ZNaUaJOP8I-po&s=wWIxhZ0sQFRqCM2a7qnyYSru8vh21i-yFlS9DiglFLE&e=>
>>> CAEN SyS Products & Solutions 
>>> <https://urldefense.proofpoint.com/v2/url?u=https-3A__caensys.com_products-2Dand-2Dsolutions_&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=ksMkvqymFO1sFCHsTbtFDMSRRxzdO2ZNaUaJOP8I-po&s=zcy1CKSquMtAvMb6ArLv6fcDY94k9m3jXSVKz6kgGrQ&e=>
>>> IOxOs Products 
>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ioxos.ch&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=ksMkvqymFO1sFCHsTbtFDMSRRxzdO2ZNaUaJOP8I-po&s=YJAckWJYg3im1sjAx40VNIKTFS7CLO9TnLUALivkW6M&e=>
>>
>>
>> -- 
>>
>>  CAEN S.p.A.  Gianni Di Maio
>>
>> *Maintenance Division Manager*
>>
>> Email: g.dimaio at caen.it <mailto:g.dimaio at caen.it>
>>
>> Skype: gdimaio_caen
>>
>> 	Cell:+393482556525 	
>>
>> *CAEN S.p.A.*
>>
>> Tel.: +39 0584 388 398
>> Fax: +39 0584 388 959
>> Email: info at caen.it <mailto:info at caen.it>
>> via Vetraia,11 • 55049 • Viareggio (LU) • Italy
>> Cod.Fisc. e p.IVA IT00864500467
>> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=xYez4K2x9z15rmeiciSi7NPPqL4bhatIr-SD73KGw8c&e=  
>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it&d=DwMF-g&c=CJqEzB1piLOyyvZjb8YUQw&r=TkJUDpm1-rWCci4nhe47nw&m=ksMkvqymFO1sFCHsTbtFDMSRRxzdO2ZNaUaJOP8I-po&s=m_dmwoWv0btIaKtYcLCUaVxX_F_Gy3P48QiYGL-j4Cw&e=> 
>>
>>
>> Le informazioni trasmesse attraverso la presente comunicazione via 
>> mail ed eventuali allegati sono da intendersi di esclusiva spettanza 
>> del destinatario. Nel caso in cui le stesse raggiungessero, per 
>> qualunque motivo, soggetti diversi dai destinatari, questi dovrebbero 
>> darne immediata notizia al mittente. In ogni caso, eventuali soggetti 
>> diversi dai legittimi destinatari della presente comunicazione sono 
>> esplicitamente diffidati da ogni utilizzazione, sia ai sensi del 
>> D.Lgs. n. 196/2003 "Codice in materia di protezione dei dati 
>> personali" sia ai sensi degli art. 616 e ss. Codice Penale che 
>> sanziona la violazione del segreto sulla corrispondenza.
>> The information contained in this transmission may contain privileged 
>> and confidential information and is intended only for the use of the 
>> person(s)named above. If you are not the intended recipient, or an 
>> employee or agent responsible for delivering this message to the 
>> intended recipient, any review, dissemination, distribution or 
>> duplication of this communication is strictly prohibited. If you are 
>> not the intended recipient, please contact the sender immediately and 
>> destroy all copies of the original message.
>>
-- 
*Greg Kibilko*
*SETS - SE Technical Sales, Inc.*
112 Tyra Lane
Townville, SC 29689
P: (864) 356-2606
CAEN Products <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.caen.it_csite&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=0uMocZ1OXK9MgOsu63nnV76fUivSIVJ9UOXj5LO3_hY&e= >
CAEN SyS Products & Solutions <https://urldefense.proofpoint.com/v2/url?u=https-3A__caensys.com_products-2Dand-2Dsolutions_&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=SD4Vkd6EWpIqscllKfqFxJkBtikFDetuYKlSzAvmjo8&e= >
IOxOs Products <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ioxos.ch&d=DwID-g&c=CJqEzB1piLOyyvZjb8YUQw&r=0dv9yTu0KREdd74L0wgLztdO3ePmhsIUc7EqYumdPxc&m=l3pdVmv-XZe0MYw1Yf7c_A1nzYM8tTqXfNXHUzmqqMQ&s=1YbkwG_KKW0Jncxn3gs-ogEBm_rdrSUTht3y6qPRkkk&e= >
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20200225/f0436529/attachment-0001.html>
    
    
More information about the Dsg-hallc_controls
mailing list