<html><body><div style="font-family: times new roman,new york,times,serif; font-size: 12pt; color: #000000"><div>Hi Mike,<br></div><div><br data-mce-bogus="1"></div><div>After a quick search, we found Allen-Bradley's manual on how to set up a Device Level Ring and what type of communication module is needed. It seems that a 1756-EN2TR module with embedded switch technology is needed.<br data-mce-bogus="1"></div><div><br data-mce-bogus="1"></div><div>In the manual, we also found that the EN2TR module is only compatible with RSLogix5000 version 17 or later (page 30).</div><div><br data-mce-bogus="1"></div><div>We double checked the compatibility with version 16 by trying to add a new EN2TR module to the SHMS PLC program and the EN2TR module is not listed as an option.<br data-mce-bogus="1"></div><div><br data-mce-bogus="1"></div><div>It seems that the best option to replace ControlNet modules is still the 1756-EN2T Ethernet/IP module since there are a few spare EN2T modules available and the EN2T modules are compatible with RSLogix5000 version 16.<br data-mce-bogus="1"></div><div><br data-mce-bogus="1"></div><div>Best regards,<br data-mce-bogus="1"></div><div>Tyler<br data-mce-bogus="1"></div><div><br data-mce-bogus="1"></div><div> <br data-mce-bogus="1"></div><hr id="zwchr" data-marker="__DIVIDER__"><div data-marker="__HEADERS__"><b>From: </b>"Mike Fowler" <fowler@jlab.org><br><b>To: </b>"dsg-hallc controls" <dsg-hallc_controls@jlab.org><br><b>Sent: </b>Tuesday, June 12, 2018 3:17:52 PM<br><b>Subject: </b>Re: [Dsg-hallc_controls] Ethernet vs Controlnet test<br></div><div><br></div><div data-marker="__QUOTED_TEXT__"><div class="moz-cite-prefix"><br>
      Hi,<br>
      <br>
      Please look into the Rockwell Automation Ethernet Device Level
      Ring.<br>
      <br>
      Thank you,<br>
      Mike<br>
      <br>
      <br>
      <br>
      <br>
      On 6/12/2018 1:14 PM, Tyler Lemon wrote:<br>
    </div>
    <blockquote cite="mid:460836661.4617096.1528823662585.JavaMail.zimbra@jlab.org">
      <div style="font-family: times new roman,new york,times,serif;
        font-size: 12pt; color: #000000">
        <div>
          <div style="font-family: times new roman,new york,times,serif;
            font-size: 12pt; color: #000000">
            <div>Hi Mike,<br>
              <br>
              No, the Ethernet modules that will be added should not
              open a security hole to the chassis.</div>
            <div><br>
            </div>
            <div>The new modules will be as secure as the existing
              Ethernet modules and will be put on the same Hall C
              subnetwork behind accelerator's firewall.<br>
            </div>
            <div><br>
            </div>
            <div>Best regards,<br>
            </div>
            <div>Tyler<br>
            </div>
            <div><br>
            </div>
            <br>
            <br>
            <br>
            <hr id="zwchr">
            <div><b>From: </b>"Mike Fowler" <a class="moz-txt-link-rfc2396E" href="mailto:fowler@jlab.org" target="_blank"><fowler@jlab.org></a><br>
              <b>To: </b>"dsg-hallc controls"
              <a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org" target="_blank"><dsg-hallc_controls@jlab.org></a><br>
              <b>Sent: </b>Tuesday, June 12, 2018 11:42:18 AM<br>
              <b>Subject: </b>Re: [Dsg-hallc_controls] Ethernet vs
              Controlnet test<br>
            </div>
            <br>
            <div>>>>1. New IP address assignment for two
              Ethernet modules in Hall C subnet.<br>
              <br>
              Does this open up security hole to the chassis?<br>
              Perhaps different Ethernet modules should be used. <br>
              <br>
              Mike<br>
              <br>
              <br>
              <br>
              <br>
              ----- Original Message -----<br>
              From: "Pablo Campero" <a class="moz-txt-link-rfc2396E" href="mailto:campero@jlab.org" target="_blank"><campero@jlab.org></a><br>
              To: "dsg-hallc controls"
              <a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org" target="_blank"><dsg-hallc_controls@jlab.org></a><br>
              Sent: Tuesday, June 12, 2018 10:57:30 AM<br>
              Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet
              test<br>
              <br>
              Hello, <br>
              <br>
              Yesterday, test was performed and results were the
              expected. <br>
              Standalone PLC test station configured back to its
              previous configuration to allow Mike continue with his
              test. <br>
              <br>
              Based in the discussion with Steve, two Controlnet modules
              will be swapped by two Ethernet modules in the "Q1" and
              "HX" PLC chassis; so in preparation for this test it will
              be required the following: <br>
              <br>
              <br>
                  1. New IP address assignment for two Ethernet modules
              in Hall C subnet. <br>
                  2. Identify Ethernet switch and ports available in
              Hall C to connect two Ethernet modules - Steve will
              contact Brad Sawatzky to identify switch. <br>
                  3. Run Ethernet cables from the switch to the modules
              respectively. <br>
                  4. Create a new SHMS PLC program, new program will
              include only the Ethernet module modifications and will
              keep all I/O module configurations/values as previously
              used by Controlnet - In progress by DSG. <br>
              <br>
              For item #1: Steve/Mike can you decide and let us know
              which of the available Ethernet modules will be used? So
              then we can get the MAC address from these modules and
              assign the IP address. <br>
              <br>
              Best Regards, <br>
              Pablo <br>
              <br>
              <br>
              <br>
              From: "Steve Lassiter" <a class="moz-txt-link-rfc2396E" href="mailto:lassiter@jlab.org" target="_blank"><lassiter@jlab.org></a> <br>
              To: "Pablo Campero" <a class="moz-txt-link-rfc2396E" href="mailto:campero@jlab.org" target="_blank"><campero@jlab.org></a> <br>
              Cc: "dsg-hallc controls"
              <a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org" target="_blank"><dsg-hallc_controls@jlab.org></a> <br>
              Sent: Monday, June 11, 2018 11:51:45 AM <br>
              Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet
              test <br>
              <br>
              Hi, <br>
              Sounds Good. <br>
              I would like to look over the setup and test. Lets shoot
              for 1:30pm today in ted 1544. <br>
              <br>
              Did the PLC down time include time to re-schedule the PLC
              on networxs? <br>
              <br>
              Steven <br>
              <br>
              <br>
              From: "Pablo Campero" <a class="moz-txt-link-rfc2396E" href="mailto:campero@jlab.org" target="_blank"><campero@jlab.org></a> <br>
              To: "dsg-hallc controls"
              <a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org" target="_blank"><dsg-hallc_controls@jlab.org></a> <br>
              Sent: Monday, June 11, 2018 11:26:11 AM <br>
              Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet
              test <br>
              <br>
              <br>
              <br>
              Hello Steve and Mike, <br>
              <br>
              <br>
              <br>
              From DSG's point of view the pre-test requested has been
              completed. <br>
              <br>
              <br>
              <br>
              For the test three chassis were configured as follow: <br>
              <br>
              Chassis #1: (Master chassis which has the controller Stand
              Alone PLC) <br>
              <br>
              Chassis #2 : Slave 1; configured with Controlnet module
              for interface communication and I/O modules <br>
              <br>
              Chassis #3: Slave 2; configured initially with a
              Controlnet module (to then be swapped by a Ethernet
              module) and I/O modules. <br>
              <br>
              <br>
              <br>
              Two PLC ACD. files (PLC programs) have been created and
              used for this test. The first PLC program has the all
              Controlnet configurations between Master and Slaves
              chassis and is simulating the actual configuration in the
              SHMS PLC systems; the second PLC program contains the
              combined network configurations with Slave 1 chassis using
              a Controlnet module, Slave 2 with Ethernet module, this
              chassis #3 is simulating the changes that needs to be
              implemented. <br>
              <br>
              <br>
              <br>
              The results of the test showed that Ethernet module work
              without any problem when it was used to replace the
              Controlnet module. <br>
              <br>
              The system is able to run with a combined network
              configuration (Ethernet and Controlnet modules) with no
              problems. The down period (PLC off line) measured in the
              test for the PLC was less than 1 min, this is the time
              needed to download the new version of the PLC program
              which includes the implementation of the Ethernet module
              the SHMS PLC I/O chassis. So based in this test, we can
              follow the previous procedure mentioned (6 steps) and
              after downloading of the new version of the PLC program to
              the SHMS PLC shouldn't be any error. <br>
              <br>
              <br>
              <br>
              If you want to check the test running, please let us know
              and we can go over it today and be done with this check to
              allow Mike continue with his test in the Standalone PLC
              test station. <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              Best Regards, <br>
              <br>
              Pablo <br>
              <br>
              <br>
              <br>
              <br>
              From: "Pablo Campero" <a class="moz-txt-link-rfc2396E" href="mailto:campero@jlab.org" target="_blank"><campero@jlab.org></a> <br>
              To: "dsg-hallc controls"
              <a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org" target="_blank"><dsg-hallc_controls@jlab.org></a> <br>
              Sent: Friday, June 8, 2018 5:05:13 PM <br>
              Subject: [Dsg-hallc_controls] Ethernet vs Controlnet test
              <br>
              <br>
              Hello, <br>
              <br>
              To test the performance of the Ethernet vs Controlnet for
              the SHMS PLC systems, Amanda, Tyler and I have done the
              following: <br>
              <br>
              <br>
                  1. Set up standalone PLC to mimic how the SHMS PLC
              system is set up with the controller and I/O modules in
              different chassis. <br>
                  2. Added DSG-PLC chassis to the standalone PLC system
              using initially Controlnet network for a total of three
              chassis (1 controller chassis, and 2 I/O chassis) <br>
                  3. Began development of PLC program to very test
              system works <br>
              <br>
              Next week DSG plans to swap the Controlnet module with
              Ethernet module to verify that Standalone PLC can run with
              one I/O chassis using an Ethernet module and a second I/O
              chassis using a Controlnet module. <br>
              <br>
              <br>
              Best Regards, <br>
              Pablo <br>
              <br>
              _______________________________________________ <br>
              Dsg-hallc_controls mailing list <br>
              <a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank">Dsg-hallc_controls@jlab.org</a> <br>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a> <br>
              <br>
              <br>
              _______________________________________________ <br>
              Dsg-hallc_controls mailing list <br>
              <a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank">Dsg-hallc_controls@jlab.org</a> <br>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a> <br>
              <br>
              <br>
              _______________________________________________<br>
              Dsg-hallc_controls mailing list<br>
              <a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank">Dsg-hallc_controls@jlab.org</a><br>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a><br>
              _______________________________________________<br>
              Dsg-hallc_controls mailing list<br>
              <a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank">Dsg-hallc_controls@jlab.org</a><br>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a><br data-mce-bogus="1"></div>
          </div>
          <br>
        </div>
      </div>
    </blockquote>
    <p><br>
    </p>
  

<br>_______________________________________________<br>Dsg-hallc_controls mailing list<br>Dsg-hallc_controls@jlab.org<br>https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls<br></div></div></body></html>