>>What should happen to the power supply should an interlock
occur? Meaning if an interlock occurs and the regulation is
stopped...<br>
<br>
If an interlock should occur the MPS will ramp down. The
regulation program should stop and return to standby, waiting for
new input from the operator.<br>
<br>
Cheers,<br>
Mike<br>
<br>
<br>
<br>
<br>
<br>
On 10/18/2018 9:45 AM, Amanda Hoebel wrote:<br>
</div>
<blockquote type="cite"
cite="mid:649945316.7005695.1539870356723.JavaMail.zimbra@jlab.org">
<meta http-equiv="content-type" content="text/html; charset=utf-8">
<div style="font-family: arial, helvetica, sans-serif; font-size:
12pt; color: #000000">
<div data-marker="__QUOTED_TEXT__">
<div style="font-family: arial, helvetica, sans-serif;
font-size: 12pt; color: #000000">
<div>Hi Mike,<br data-mce-bogus="1">
</div>
<div><br data-mce-bogus="1">
</div>
<div>It does look like there was a tag and operator missing
from the pdf I had sent you. They exist in the version of
the program I was looking at. Before I send the newest
version I have a question on one of the program
requirements. In your comments you stated that: </div>
<div><br data-mce-bogus="1">
</div>
<div>1. If an Interlock occurs the regulation is not
stopped. Need this.<br style="" data-mce-style="">
2. If the MPS is ramping and the operator stops the
regulation, the I_coarse value should be sent to the MPS.
(Stop where it is)<br data-mce-bogus="1">
</div>
<div><br data-mce-bogus="1">
</div>
<div>What should happen to the power supply should an
interlock occur? Meaning if an interlock occurs and the
regulation is stopped, are you saying the I_coarse value
should be sent to the MPS just as it should be done if the
operator stops the regulation?<br data-mce-bogus="1">
</div>
<div><br data-mce-bogus="1">
</div>
<div>Regards,<br>
</div>
<div>Amanda<br>
</div>
<br>
<br>
<hr id="zwchr">
<div><b>From: </b>"Mike Fowler" <a class="moz-txt-link-rfc2396E" href="mailto:fowler@jlab.org"><fowler@jlab.org></a><br>
<b>To: </b>"dsg-hallc controls"
<a class="moz-txt-link-rfc2396E" href="mailto:dsg-hallc_controls@jlab.org"><dsg-hallc_controls@jlab.org></a><br>
<b>Sent: </b>Friday, September 28, 2018 3:45:32 PM<br>
<b>Subject: </b>Re: [Dsg-hallc_controls] Quadrupole field
regulation<br>
</div>
<br>
<div>
<div class="moz-cite-prefix">>>>the operator
inputs an I_target value and then selects to start
regulation, the I_target value will be stored as
Last_I_sent<br>
<br>
Perhaps I am missing the code where start regulation
triggers where Last_I_Sent is made equal to I_target.<br>
<br>
Mike<br>
<br>
<br>
<br>
<br>
<br>
On 9/28/2018 3:02 PM, Amanda Hoebel wrote:<br>
</div>
<blockquote
cite="mid:662426473.30430128.1538161322591.JavaMail.zimbra@jlab.org">
<div style="font-family: arial, helvetica, sans-serif;
font-size: 12pt; color: #000000">
<div>If the operator inputs an I_target value and then
selects to start regulation, the I_target value will
be stored as Last_I_sent (on the function block
diagram). On the ladder logic, I_coarse is basically
being compared to I_target, since I_target and
Last_I_sent would be the same value. The program
would still work with the PSU starting from zero.<br>
</div>
<div><br>
</div>
<div><br>
</div>
<hr id="zwchr">
<div><b>From: </b>"Mike Fowler" <a
class="moz-txt-link-rfc2396E"
href="mailto:fowler@jlab.org" target="_blank"
moz-do-not-send="true"><fowler@jlab.org></a><br>
<b>To: </b>"dsg-hallc controls" <a
class="moz-txt-link-rfc2396E"
href="mailto:dsg-hallc_controls@jlab.org"
target="_blank" moz-do-not-send="true"><dsg-hallc_controls@jlab.org></a><br>
<b>Sent: </b>Friday, September 28, 2018 2:28:11 PM<br>
<b>Subject: </b>Re: [Dsg-hallc_controls] Quadrupole
field regulation<br>
</div>
<div><br>
</div>
<div>
<div class="moz-cite-prefix">Condition one: PSU
starting from zero<br>
<br>
Operator> Inputs an I_target and I_MOL value.<br>
PLC> Checks I_target if in limits, sets the
MPS_Wa_Value<br>
Operator> Start regulation<br>
PLC> Compares analog I_coarse to Last_I_Sent
which is assumed to be zero.<br>
If I_coarse > Last_I_Sent the code
sends MPS_Wa_Value to PSU. Note: analog I_coarse
value could be non zero and the MOL value is not
sent.<br>
PLC> Waits for I_coarse to be equal to MOL
value +/-1%. Was the MOL value ever sent?<br>
<br>
Mike<br>
<br>
<br>
<br>
<br>
<br>
On 9/28/2018 2:00 PM, Amanda Hoebel wrote:<br>
</div>
<blockquote
cite="mid:1519482268.29539666.1538157629217.JavaMail.zimbra@jlab.org">
<div style="font-family: arial, helvetica,
sans-serif; font-size: 12pt; color: #000000">
<div>The operator would input an I_target and
I_MOL value, then select to start regulation.<br>
</div>
<div><br>
</div>
<div><br>
</div>
<hr id="zwchr">
<div><b>From: </b>"Mike Fowler" <a
class="moz-txt-link-rfc2396E"
href="mailto:fowler@jlab.org"
target="_blank" moz-do-not-send="true"><fowler@jlab.org></a><br>
<b>To: </b>"dsg-hallc controls" <a
class="moz-txt-link-rfc2396E"
href="mailto:dsg-hallc_controls@jlab.org"
target="_blank" moz-do-not-send="true"><dsg-hallc_controls@jlab.org></a><br>
<b>Sent: </b>Friday, September 28, 2018
1:54:31 PM<br>
<b>Subject: </b>Re: [Dsg-hallc_controls]
Quadrupole field regulation<br>
</div>
<div><br>
</div>
<div>
<div class="moz-cite-prefix"><br>
Hi,<br>
<br>
What is the sequence of inputs from the
operator?<br>
<br>
Mike<br>
<br>
<br>
<br>
On 9/28/2018 1:30 PM, Amanda Hoebel wrote:<br>
</div>
<blockquote
cite="mid:1323893506.29082462.1538155802191.JavaMail.zimbra@jlab.org">
<div style="font-family: arial, helvetica,
sans-serif; font-size: 12pt; color:
#000000">
<div>
<div style="font-family: arial,
helvetica, sans-serif; font-size:
12pt; color: #000000">
<div>Hi Mike,<br>
</div>
<br>
<div>I have some questions/comments
(in blue) on some of your comments
for the current loop regulation.<br>
</div>
<br>
<div>4. If the analog signal I_coarse
is less than the Last_I_Sent by even
a small fraction the MOL value is
used.<br>
</div>
<div><span style="color: rgb(0, 0,
255);">Yes, as the PSU would be
ramping up, even if it's by a
small amount. This would only
occur if someone were to set an
I_target/Last_I_Sent value that
was very close to what the power
supply was already at. If that is
not the correct method, what
should be done instead?</span><br>
</div>
<br>
<div>7. Consider this:<br style="">
If I_coarse is equal to Last_I_Sent
+/- a few amps<br style="">
true, MPS is at setpoint<br
style="">
false, The MPS is still ramping,
something happened, or the MPS
tripped and the Last_I_Sent was not
updated. (Interlock?)<br style="">
or the window is too
small. Determine what to do.</div>
<div><span style="color: rgb(0, 0,
255);">I am unsure of what you are
suggesting. I will implement a
condition where the loop stops if
there is an interlock (as per
comment #1) and can add a case
where the program continues to the
next rung if the PSU_Ready is
True, in the event that the window
is too small. Any other problem
that could arise seems like it
would be related to the PSU
itself, not the program. The
program does not ramp the PSU and
stop ramp only if the current
falls within the window. The PSU
will stop at the set point given
(no runaway condition possible).</span><br>
</div>
<br>
<div>8. Compare Q1_I_Target to
Last_I_Sent to determine ramp
direction instead of the analog
I_coarse.</div>
<div><span style="color: rgb(0, 0,
255);">Q1_I_Target and Last_I_Sent
cannot be compared for ramp
direction, as they will be the
same value as each other on the
ladder logic when the regulation
routine is enabled.</span><br>
</div>
<div><span style="color: rgb(0, 0,
255);"><br>
</span></div>
<div><span style="color: rgb(0, 0,
0);">Regards,<br>
</span></div>
<div><span style="color: rgb(0, 0,
0);">Amanda<br>
</span></div>
<br>
<hr id="zwchr">
<div><b>From: </b>"Amanda Hoebel" <a
class="moz-txt-link-rfc2396E"
href="mailto:amandah@jlab.org"
target="_blank"
moz-do-not-send="true"><amandah@jlab.org></a><br>
<b>Sent: </b>Wednesday, September
26, 2018 10:04:46 AM<br>
<b>Subject: </b>Re:
[Dsg-hallc_controls] Quadrupole
field regulation<br>
</div>
<br>
<div>
<div style="font-family: arial,
helvetica, sans-serif; font-size:
12pt; color: #000000">
<div>
<div style="font-family: arial,
helvetica, sans-serif;
font-size: 12pt; color:
#000000"><br>
<hr id="zwchr">
<div><b>From: </b>"Mike
Fowler" <a
class="moz-txt-link-rfc2396E"
href="mailto:fowler@jlab.org" target="_blank" moz-do-not-send="true"><fowler@jlab.org></a><br>
<b>To: </b>"dsg-hallc
controls" <a
class="moz-txt-link-rfc2396E"
href="mailto:dsg-hallc_controls@jlab.org" target="_blank"
moz-do-not-send="true"><dsg-hallc_controls@jlab.org></a><br>
<b>Sent: </b>Tuesday,
September 25, 2018 10:37:25
AM<br>
<b>Subject: </b>Re:
[Dsg-hallc_controls]
Quadrupole field regulation<br>
</div>
<br>
<div>
<div class="moz-cite-prefix">Hi,<br>
<br>
Comments.<br>
<br>
The ability to manually
input a current and send
it without a MOL value has
been removed. <br>
Must be included.<br>
<br>
Cheers,<br>
Mike<br>
<br>
<br>
<br>
On 9/20/2018 9:12 AM,
Amanda Hoebel wrote:<br>
</div>
<blockquote
cite="mid:59817053.2238488.1537449142333.JavaMail.zimbra@jlab.org">
<div style="font-family:
arial, helvetica,
sans-serif; font-size:
12pt; color: #000000">
<div>Hi Mike,<br>
</div>
<div><br>
</div>
<div>I have attached
pdfs of the field
regulation routine for
HMS Q1. If this is
correct I will make
the routines for HMS
Q2 and Q3, and for the
quads in SHMS.<br>
</div>
<div><br>
</div>
<div>Regards,<br>
</div>
<div>Amanda<br>
</div>
</div>
<br>
<fieldset
class="mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
Dsg-hallc_controls mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a>
</pre>
</blockquote>
<p><br>
</p>
<br>
_______________________________________________<br>
Dsg-hallc_controls mailing
list<br>
<a
class="moz-txt-link-abbreviated"
href="mailto:Dsg-hallc_controls@jlab.org" target="_blank"
moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a><br>
<a
class="moz-txt-link-freetext"
href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls"
target="_blank"
moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a><br>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
Dsg-hallc_controls mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a>
</pre>
</blockquote>
<p><br>
</p>
<br>
_______________________________________________<br>
Dsg-hallc_controls mailing list<br>
<a class="moz-txt-link-abbreviated"
href="mailto:Dsg-hallc_controls@jlab.org"
target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a><br>
<a class="moz-txt-link-freetext"
href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls"
target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a><br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
Dsg-hallc_controls mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a>
</pre>
</blockquote>
<p><br>
</p>
<br>
_______________________________________________<br>
Dsg-hallc_controls mailing list<br>
<a class="moz-txt-link-abbreviated"
href="mailto:Dsg-hallc_controls@jlab.org"
target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a><br>
<a class="moz-txt-link-freetext"
href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls"
target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a><br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
Dsg-hallc_controls mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org" target="_blank" moz-do-not-send="true">Dsg-hallc_controls@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls" target="_blank" moz-do-not-send="true">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a>
</pre>
</blockquote>
<p><br>
</p>
<br>
_______________________________________________<br>
Dsg-hallc_controls mailing list<br>
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org">Dsg-hallc_controls@jlab.org</a><br>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a></div>
</div>
<br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Dsg-hallc_controls mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Dsg-hallc_controls@jlab.org">Dsg-hallc_controls@jlab.org</a>
<a class="moz-txt-link-freetext" href="https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls">https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls</a>
</pre>
</blockquote>
<p><br>
</p>
</body>
</html>