I guess the PXI is close enough to a PLC to use this mailing list?
Here's the first report of the trip: https://logbooks.jlab.org/entry/3511895
Follow the various backlinks on each entry to see follow-ups.
Checking the solenoid logbook might be easier? https://logbooks.jlab.org/book/hdsolenoid
The root cause seems to be a failed network port on the PXI. First causing the timeout on the PLC and causing the dump, later swapped network configurations which prevented it from rebooting cleanly.
Currently the ports have been swapped and it is running without issue.
I'm currently looking into getting a spare/replacement controller.
The one being used now is nearing EOL so we'll probably end up ordering a different model, waiting on part # and quote from NI.
----- Original Message -----
> From: "Amrit Yegneswaran" <yeg at jlab.org>
> To: "dsg-halld plc" <dsg-halld_plc at jlab.org>
> Cc: "rossi patrizia" <rossi at jlab.org>
> Sent: Tuesday, January 16, 2018 8:00:14 PM
> Subject: [Dsg-halld_plc] mailing list for halld plc work
> this was the mailing list i was talking about.
> please post requests/activities for hall d magnet plc on this mailing list.
> give it a shot.