[Eng-div] Reminder to Engineering Staff
Gayle Coleman
sundeen at jlab.org
Wed Jan 2 14:06:38 EST 2013
/*The following message is being sent on behalf of Henry Robertson,
Engineering DSO:*/
*Just a reminder about the use of GFCI devices:
***/
(GFCI circuits are always required in JLab tunnel environments and most
other concrete/slab structures!)
/*
ES&H Manual
6200 Appendix T4* *- General Electrical Safety Guidelines*
*4.2**Ground-Fault Circuit Interrupter
<http://www.jlab.org/ehs/ehsmanual/Glossary.htm#GFCIDef> (GFCI)*
GFCI is a device intended for the protection of personnel.It de-energize
a circuit, or portion thereof, within an established period of time when
current to ground exceeds approximately 6mA.A GFCI is required:
·Per the National Electrical Code.They are installed in all new
construction and renovation projects as required.
·Where 125-volt single-phase; and 15- and 20-ampere receptacles are
installed (i.e., bathrooms, kitchens, rooftops, outdoors, and within six
feet of the outside edge of a sink).
·For all receptacle outlets (including extension cords, and temporary
wiring used to supply power to equipment during construction,
remodeling, maintenance, repair, or demolition of buildings, structures,
or equipment, or similar activities.)
·For use with:
oCord-and-plugged vending machines (installed after 1/1/2005).
oElectric drinking fountains (installed after 1/1/2008).
oPortable generators -- for all 125-volt single-phase 15-, 20-, and
30-ampere receptacles that are in use by personnel.
·When supplying temporary power, with the use of extension cords, in a
damp or wet location.
·When supplying temporary power for Jefferson Lab sponsored events --
for all 125-volt single-phase 15-, 20-, and 30-ampere receptacles that
are in use by personnel.
*4.2.1**Testing GFCI*
Jefferson Lab recommends that GFCI receptacles be tested in accordance
with manufacturer's recommendations, periodically, and before using a
device after an extended period of time.
*4.2.2**Types of GFCIs*
*4.2.2.1**Receptacle:*A GFCI receptacle is used in place of a standard
outlet (see Figure 1.GFCI Receptacle).These are generally found near
water sources (e.g., kitchens, bathrooms, etc.).
*Figure 1.**GFCI Receptacle*
gfci receptacle1gfci receptacle2
*4.2.2.2**Portable:*A portable GFCI is used to provide temporary power
from an unprotected outlet.They are tested prior to each use (see Figure
2.Portable GFCIs).
*Figure 2.**Portable GFCIs*
Portable GFCI
*4.2.2.3**Circuit Breaker:*A GFCI circuit breaker controls an entire
circuit on the main panel board.In the event of a ground fault, short
circuit, or overload the breaker trips and shuts off electricity to
circuit.Only those persons who have been trained by a qualified
electrical worker are authorized to reset GFCI circuit breakers.Contact
Facilities Management (x7400) for assistance if electricity is
interrupted to your work area.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: https://mailman.jlab.org/pipermail/eng-div/attachments/20130102/dde6f355/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2349 bytes
Desc: not available
Url : https://mailman.jlab.org/pipermail/eng-div/attachments/20130102/dde6f355/attachment-0003.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2124 bytes
Desc: not available
Url : https://mailman.jlab.org/pipermail/eng-div/attachments/20130102/dde6f355/attachment-0004.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5952 bytes
Desc: not available
Url : https://mailman.jlab.org/pipermail/eng-div/attachments/20130102/dde6f355/attachment-0005.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: sundeen.vcf
Type: text/x-vcard
Size: 227 bytes
Desc: not available
Url : https://mailman.jlab.org/pipermail/eng-div/attachments/20130102/dde6f355/attachment-0001.vcf
More information about the Eng-div
mailing list