[Esr-users] [New Logentry] Root Cause Search for ESR Trip 2/6/2018
kashy at jlab.org
kashy at jlab.org
Tue Feb 6 22:45:01 EST 2018
Logentry Text:
--
I looked though many signals in the Mya Viewer Archive. I found the following:
In time order (times per the data logger, there may be time shifts due to data collection rates etc.)
At 16:34:40 the lead flow of the Hall C SHMS HB magnet went from 100 steady up to 113 then back down to 100 at 13:35:17
At 16:35:19 the helium level in the Hall C SHMS HB went from 70 to 51
At 16:35:26 the lead flow in the Hall C SHMS Q3 went form 88 to 85 (not a big change)
At 16:35:37 the three pressure sensors on the quench headers of Halls A, B, C (CPI603QA, QB, QC) started to slowly rise from their flatline values
At 16:35:40 the helium level of the Hall C SHMS Q3 went from 70% to 35%
At 16:35:48 the Hall B Solenoid magnet resevoir started to slowly loose helium level
At 16:36:02 the Hall A Right Dipole started to slowly ramp down but at 16:37:31 it started to ramp up
At 16:37:42 the helium level in the Hall A right dipole started to climb then at 16:39:09 ti dopped form 96% to 26%
At 16:44:56 ESR Turbines T1 and T2 tripped
I can't make any firm conclusions, because I do not know the accuracy of the time stamps on the above data...
---
This is a plain text email for clients that cannot display HTML. The full logentry can be found online at https://logbooks.jlab.org/entry/3528416
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/esr-users/attachments/20180206/5bf51219/attachment.html>
More information about the Esr-users
mailing list