[Esr-users] More SHMS Q2 dump test

Steven Lassiter lassiter at jlab.org
Mon Oct 28 14:15:50 EDT 2019


Hi Joe,

 Eric S, Amy C and myself were present during the test, beside the magnet when the quench-back occurred. There was only one Quench-back event within Hall C at around 10:50a this morning. After that event, the magnet power supply was turned off to allow magnets to recover.

SHMS Q2 is slowly re-filling.

Steven
________________________________
From: Joe Wilson <jwilson at jlab.org>
Sent: Monday, October 28, 2019 1:58 PM
To: Probir Ghoshal <ghoshal at jlab.org>; Steven Lassiter <lassiter at jlab.org>; Eric Sun <qsun at jlab.org>
Cc: Cryo <esr-users at jlab.org>
Subject: Re: More SHMS Q2 dump test


Steven,

How did you confirm that no relief valve lifted, because ESR corrective actions may have been needed? As 1330 28Oct19, the ESR warm return line pressures have not yet recovered from the events at 1055 and 1153.

Thanks!



-----------------

Joe D. Wilson, Jr.

Cryogenic Operations Engineer



Jefferson Lab

www.jlab.org<http://www.jlab.org/>

office desk: 757-269-7722

jwilson at jlab.org


________________________________
From: Esr-users <esr-users-bounces at jlab.org> on behalf of Probir Ghoshal <ghoshal at jlab.org>
Sent: Monday, October 28, 2019 11:13 AM
To: Steven Lassiter <lassiter at jlab.org>; Eric Sun <qsun at jlab.org>
Cc: Cryo <esr-users at jlab.org>
Subject: Re: [Esr-users] More SHMS Q2 dump test

Steve, Eric,

What's the temperature of the magnet and shied went up to?
Eric - what is the hot spot temp you expected with fast dump from full current..?
I am curious about the data..!
Speak to you later.

Regards
Probir

________________________________
From: Esr-users <esr-users-bounces at jlab.org> on behalf of Steven Lassiter <lassiter at jlab.org>
Sent: Monday, October 28, 2019 11:02 AM
To: Eric Sun <qsun at jlab.org>; Cryo <esr-users at jlab.org>
Subject: Re: [Esr-users] More SHMS Q2 dump test

At the highest current the dump test induce Quench back and pressures in SHMS Q2 rose to 4.757atm
Almost to the relief setting.

System is recovering now.

testing is concluded.

Steven
________________________________
From: Esr-users <esr-users-bounces at jlab.org> on behalf of Eric Sun <qsun at jlab.org>
Sent: Monday, October 28, 2019 9:51 AM
To: Cryo <esr-users at jlab.org>
Subject: [Esr-users] More SHMS Q2 dump test

Howdy,

Hall C will be performing more Dump test of the SHMS Q2 magnet today.
Do not expect any cryo issues from the test.

Thanks a lot

Eric


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/esr-users/attachments/20191028/567fc325/attachment-0001.html>


More information about the Esr-users mailing list