[Esr-users] [New Logentry] Follow-up Re: Preparing for CLAS 12 Torus Burp
kashy at jlab.org
kashy at jlab.org
Mon Oct 12 16:15:02 EDT 2020
Logentry Text:
--
I reduced the set value and some PID parameters and got the flow to go up to ~5-6 g/s which is good as it will replace much of the flow that the torus will not have once isolated.
I took the temperature setpoint from 7.1 down to 6.1, it remained very stable between 6.8 and 6.4 so we will probably start at around 6.4K as the setpoint.
I returned all parameters and the system looks to be stable.
---
This is a plain text email for clients that cannot display HTML. The full logentry can be found online at https://logbooks.jlab.org/entry/3854680
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/esr-users/attachments/20201012/3d16995c/attachment.html>
More information about the Esr-users
mailing list