Cryo needed to protect the ESR system from too much load so they throttled the max position of the supply valve EV6711B. 
Flow was running 10g/s farily stabily for about 1 hr prior to that.
This dropped the supply pressure of the SC Helium, so we changed a control loop setpoint to get us less flow but at a higher pressure which is needed to force flow through the long path of the CLAS12 Torus 4 K circuit. 
---