[Utility Outage] Scheduled HVAC Outage - 10/12/2016 08:00
    Carroll W. Jones 
    jonesc at jlab.org
       
    Mon Oct 10 19:35:49 EDT 2016
    
    
  
The following HVAC Outage has been Confirmed:
Outage:      Testing and Balancing of ARC Building AHU-1, AHU-5, Chiller, and Boiler System
Proposed By: Carroll W. Jones
Start Time:  10/12/2016 08:00
End Time:    10/12/2016 19:30
Description/Impacts:
Testing and balancing (TAB) activities were be conducted last Friday 10-7-16, but only AHU-5 balancing activities were completed which only impacted non-lab areas located within the three story lab area.  The remaining TAB activities listed below will resume Wednesday morning 10-12-16.
AHU-1 balancing activities will require all labs to be switched to occupied (of standard) mode of operation which is maximum air flow.  Impact to lab area operations should be minimal.
Balancing activities of the new cooling system chillers require AHU-1 and AHU-5 to be forced into full cooling during measurements.  Lab area discharge air from AHU-1 will be colder than normal during measurements, but the lab reheat system should compensate for the cooler main supply air.
The laboratory chiller system used for equipment cooling will not be impacted.  The laboratory chiller is not part of the work scope.
Boiler system balancing requires that all heating valves throughout the ARC Buildings (labs, conferences rooms, offices, etc.) be commanded fully open during measurements.  The impact will be areas will become warm during testing.  Boiler System TAB activities will begin at 5 PM due to minimize the potential impact on occupants and activities in various areas.
For additional information or clarification, please contact Carroll Jones at 757-876-1778.
Impacted Areas:
	ARC: Advanced Research Center
For more details, visit the webpage listed below:
https://cc.jlab.org/cgi-bin/infrastructure/Outage/OutageView?ident=3
    
    