[Hallb-engineering] Fwd: Lesson Learned "Lockout/Tagout Device Condition Transient Reactor Test Facility (TREAT)"
Douglas Tilles
tilles at jlab.org
Fri Sep 2 11:01:35 EDT 2016
FYI
----- Forwarded Message -----
From: "mbailey" <mbailey at jlab.org>
To: "mbailey" <mbailey at jlab.org>
Sent: Friday, September 2, 2016 11:00:15 AM
Subject: Lesson Learned "Lockout/Tagout Device Condition Transient Reactor Test Facility (TREAT)"
Jefferson Lab Lessons Learned : Print Lesson
Lockout/Tagout Device Condition Transient Reactor Test Facility (TREAT)
Statement of Lessons Learned
On January 14, 2016, a TREAT Facility Representative questioned the adequacy of a locking device along with its ability to prevent operation of the associated 120v breaker due to slight play in the lockout configuration. It was theorized that a reasonable scenario could result in a condition that would allow the breaker to be shut with the locking device in place.
The investigation resulting from this theory showed that when fully closed the locking device did prevent operation of the breaker.
Discussion of Activities
The locking device was from different manufacturer than those authorized. It looked similar but did not have the same physical dimensions or operability functions.
Analysis
All Authorized Workers on the LO/TO confirmed that when the locking device was initially installed all had verified the installation and adequacy of the device; and that even though the system had been locked out it was in its normal configuration as work had not started.
Recommended Actions
Below are the consequences of the above event. They are provided for information and discussion purposes only.
The Operations Manager contacted the Facility Area Supervisor to confirm that no work was being performed under the LO/TO in question and removed any effected work from the approved Plan of the Day.
An inspection of all installed LO/TOs was performed to ensure no other devices exhibited the same issue.
All similar locking devices were checked to ensure they provided full locking capability. The failed locking device, while of the same design, was from a different manufacturer and had a slightly smaller diameter shackle which allowed the clearance to shut the breaker.
The workers removed their personal locks from the suspect locking device and replaced it with one that clearly prevented operation of the breaker.
JLab Preventive Measures
(Jefferson Lab�s Subject Matter Expert has read and approved this lesson.)
In accordance with Jefferson Lab�s ES&H Manual Chapter 6110 Lock, Tag, Try Program only approve and authorized locks and tags are to be used for locking out of systems. Samples of pproved locks and Tags can be found at https://www.jlab.org/ehs/ehsmanual/Glossary.htm#LTTDef .
Contact Todd Kujawa, Electrical Safety Engineer at x7006 if you have questions regarding the adequacy of a lock, or you see an unapproved lock on a system.
Comments
9/2/2016 9:17:29 AM by Bailey, Mary Jo
Submitted to those with SAF603A: ELECTRICAL SAFETY AWARENESS
Summary Lesson ID: 963
Status: OK
Doc ID: 2016-JLAB-963
Priority: Best Practice
Safety Related: YES
Originator: Bailey, Mary Jo
Issued: 9/2/2016 9:13:38 AM
Approved By: Bailey, Mary Jo
Approved On: 9/2/2016 9:17:29 AM
Source: DOECRD
Location: INL
Cost Savings:
Contact: L. Kinghorn/ 208-533-889 TREAT at Idaho National Laboratory
Queued Emails: 0
Sent Emails: 0
Viewings: 1 times Attachments
* DOE - LTT1.pdf
* ES&H Manual Chapter 6110 Appendix T1 Lock, Tag, Try (LTT) Procedure
Hazard Issues
* Lock, Tag, Try
Skills
* SAF603A: ELECTRICAL SAFETY AWARENESS
Distribution/Notification
* *Division Safety Officers (DSOs)
* *Safety Wardens
* *DOE Notification
* *ESH&Q Liaisons
Do you have a lesson learned you would like to contribute? Contact the Lesson Learned Coordinator .
More information about the Hallb-engineering
mailing list