[Hallb-engineering] [New Logentry] Follow-up Re: Ramp to 1000 Amps - Review of voltage data
rfair at jlab.org
rfair at jlab.org
Tue Sep 12 16:25:02 EDT 2017
Logentry Text:
--
Review of the voltage data following the 'event' at 932 A (while ramping to 1000 A at 0.7 A/s) indicated the following:
VT18 (splice between VCL B and the superconducting bus within the SST - i.e. in liquid helium) developed a voltage spike (approx. 600 mV peak).
VT18 is part of the hardwired QD protection system which has voltage thresholds ranging form 80 mV to 125 mV.
It is likely that this voltage spike triggered the QD system which then initiated a fast dump.
The fast dump in turn produced eddy current heating in the magnet coils, causing Coil 3 to quench.
Coil 3 was the only coil to indicate a positive (resistive) voltage while all the other coils indicated inductive voltages.
All the helium in the magnet reservoir boiled-off.
It is possible that this splice joint moved somehow, producing this voltage spike.
---
This is a plain text email for clients that cannot display HTML. The full logentry can be found online at https://logbooks.jlab.org/entry/3484224
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/hallb-engineering/attachments/20170912/d6d5e374/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2017-09-12 at 3.12.39 PM.png
Type: image/png
Size: 265015 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/hallb-engineering/attachments/20170912/d6d5e374/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2017-09-12 at 3.37.50 PM.png
Type: image/png
Size: 237777 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/hallb-engineering/attachments/20170912/d6d5e374/attachment-0003.png>
More information about the Hallb-engineering
mailing list