[Hallb-engineering] DP8620VCLDP

Brian Eng beng at jlab.org
Tue May 14 12:10:24 EDT 2024


That Cernox should be LV Chassis #1 J7 connector.

On May 14, 2024, at 12:08 PM, David Kashy <kashy at jlab.org> wrote:

I noticed the TR8122A about 1.5 hrs ago and told Probir, he went to the Hall to troubleshoot.
________________________________
From: Brian Eng <beng at jlab.org>
Sent: Tuesday, May 14, 2024 12:06 PM
To: Eugene Pasyuk <pasyuk at jlab.org>
Cc: David Kashy <kashy at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>; Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

TR8122A is reading bad at the cRIO, I suspect reseating the connector will fix the values. Maybe doing it at the LV chassis will be enough?

I have a meetings for a while so maybe someone else will be able to go down and do that?

On May 14, 2024, at 11:44 AM, Eugene Pasyuk <pasyuk at jlab.org> wrote:

Two warnings remain LL8120SC overfilled and TR8122A chimney splice. The latter shows strange behavior, jumping between 4.5 K and 34 K every second.

-Eugene





________________________________
From: Hallb-engineering <hallb-engineering-bounces at jlab.org> on behalf of Eugene Pasyuk via Hallb-engineering <hallb-engineering at jlab.org>
Sent: Tuesday, May 14, 2024 10:55
To: David Kashy <kashy at jlab.org>; Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

A few more warnings:
<image.png>

-Eugene





________________________________
From: Eugene Pasyuk <pasyuk at jlab.org>
Sent: Tuesday, May 14, 2024 10:51
To: David Kashy <kashy at jlab.org>; Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>; Eugene Pasyuk <pasyuk at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

There was also an alarm for the He level LL8120SC in the reservoir, which dropped to ~50%. Now it is full.

-Eugene





________________________________
From: Hallb-engineering <hallb-engineering-bounces at jlab.org> on behalf of Eugene Pasyuk via Hallb-engineering <hallb-engineering at jlab.org>
Sent: Tuesday, May 14, 2024 10:40
To: David Kashy <kashy at jlab.org>; Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

There were alarms from VCLs

-Eugene





________________________________
From: David Kashy <kashy at jlab.org>
Sent: Tuesday, May 14, 2024 10:34
To: Eugene Pasyuk <pasyuk at jlab.org>; Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

Eugene,
What were they?
Dave
________________________________
From: Eugene Pasyuk <pasyuk at jlab.org>
Sent: Tuesday, May 14, 2024 10:33 AM
To: David Kashy <kashy at jlab.org>; Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

This is the only one I see at the moment. All others are cleared.

-Eugene





________________________________
From: David Kashy <kashy at jlab.org>
Sent: Tuesday, May 14, 2024 10:31
To: Brian Eng <beng at jlab.org>; Eugene Pasyuk <pasyuk at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

Brian,
What other signals are are or were alarming?
Thanks
Dave

________________________________
From: Brian Eng <beng at jlab.org>
Sent: Tuesday, May 14, 2024 10:21 AM
To: Eugene Pasyuk <pasyuk at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; David Kashy <kashy at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

I ramped the Torus to 100 then back down to 0 to make sure MPS comms was okay. No issues there.

There's still a few cryo warnings (namely PT8115) so I'll hand it off to the Hall B folks now.
________________________________
From: Brian Eng <beng at jlab.org>
Sent: Tuesday, May 14, 2024 10:18 AM
To: Eugene Pasyuk <pasyuk at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; David Kashy <kashy at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

Not sure if someone else was also messing with it, but I set both of the VCL flows to 88 l/min which seemed to get rid of most of the alarms.

________________________________
From: Brian Eng <beng at jlab.org>
Sent: Tuesday, May 14, 2024 10:04 AM
To: Eugene Pasyuk <pasyuk at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; David Kashy <kashy at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

Torus PLC has been power cycled and is back online.

There are a handful of cryo alarms now though ... I'm guessing PIDs got reset?

Could someone check those?

________________________________
From: Eugene Pasyuk <pasyuk at jlab.org>
Sent: Monday, May 13, 2024 3:58 PM
To: Brian Eng <beng at jlab.org>; Denny Insley <dinsley at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; David Kashy <kashy at jlab.org>; Lamiaa El Fassi <elfassi at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: RE: [Hallb-engineering] DP8620VCLDP

All right then. I’ll ramp down both magnets once they terminate the beam tomorrow morning (~ 7 am). They should be off by 8:30. And we request rapid access. Let me know when you finish the reboot, and we can bring them back up.



-Eugene





From: Brian Eng <beng at jlab.org>
Sent: Monday, May 13, 2024 15:52
To: Denny Insley <dinsley at jlab.org>; Eugene Pasyuk <pasyuk at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>; David Kashy <kashy at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP



Should be fine to just do the reboot after everything is ramped down.



We need to make an access to do the reboot (have to physically power cycle it). I'd like to see if we can connect via USB before the reboot though.



I'd prefer not to upgrade the firmware in a piecemeal fashion (e.g. only the torus) and I'm not sure only 1 shift is enough time to do all of them.
________________________________
From: Denny Insley <dinsley at jlab.org<mailto:dinsley at jlab.org>>
Sent: Monday, May 13, 2024 3:31 PM
To: Eugene Pasyuk <pasyuk at jlab.org<mailto:pasyuk at jlab.org>>; Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>; David Kashy <kashy at jlab.org<mailto:kashy at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: Re: [Hallb-engineering] DP8620VCLDP



The concensus is to ramp down and reboot when we lose beam in the morning.  Brian what are your thoughts on the matter?





Sent from my Verizon, Samsung Galaxy smartphone
Get Outlook for Android<https://aka.ms/AAb9ysg>
________________________________
From: Hallb-engineering <hallb-engineering-bounces at jlab.org<mailto:hallb-engineering-bounces at jlab.org>> on behalf of Eugene Pasyuk via Hallb-engineering <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>
Sent: Monday, May 13, 2024 2:59:49 PM
To: Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>; David Kashy <kashy at jlab.org<mailto:kashy at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: Re: [Hallb-engineering] DP8620VCLDP



So, what's the verdict?



-Eugene





________________________________
From: Hallb-engineering <hallb-engineering-bounces at jlab.org<mailto:hallb-engineering-bounces at jlab.org>> on behalf of David Kashy via Hallb-engineering <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>
Sent: Monday, May 13, 2024 11:41
To: Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: Re: [Hallb-engineering] DP8620VCLDP



Hi Eugene,
I'm looking into the possible effect of the "not talking" signals.





Brian,
What signals from the solenoid are not updating in the Torus (DBX) PLC?



I see at some that are updating:
 DP8620VCLDP



B_TORUS:LHe:PV8522SR:CVAL  = PT8620
B_TORUS:LHe:PV8522SCD_Min_Min:CVAL = LL8620



Thanks Guys
Dave
________________________________
From: Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>
Sent: Monday, May 13, 2024 10:57 AM
To: David Kashy <kashy at jlab.org<mailto:kashy at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: Re: DP8620VCLDP



So I poked at the tags some more and it turns out that this one is updated on the DBox PLC, which I can still connect to. So I manually reset the error bit and this value is now updating on the PID screens.



caget B_TORUS:LHe:PV8522SR_Val:CVAL.INP
B_TORUS:LHe:PV8522SR_Val:CVAL.INP @PLC_CRYO PV8522SR_Val.CVAL



The torus PLC still isn't seeing updating values from the solenoid, but maybe we can put off the reboot until tomorrow?



________________________________
From: David Kashy <kashy at jlab.org<mailto:kashy at jlab.org>>
Sent: Monday, May 13, 2024 10:49 AM
To: Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: DP8620VCLDP



Just as a reminder,
This signal is a calculated value base on two pressure sensors.
the math goes as follows:



DP8620VCLDP =PT8620-PT8571



There is a similar setup of
DP8670MAGDP = PT8670-PT8571



Dave

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/hallb-engineering/attachments/20240514/7e397a53/attachment-0001.html>


More information about the Hallb-engineering mailing list