Hello Scot, 

I've been working on the configuration I/O modules for the Solenoid PLC and I have a couple of questions, and I would like to know if you or someone else can help me. 
1. Is there a POINT I/O system for the solenoid? 

If so : 
2. How many I/O modules it is going to have? 
3. Do we have a drawing or spreadsheet for that ? 
4. Do we have already set up an IP address for this POINT I/O system? 



We've been looking at the drawings and we find some discrepancies regard to drawings B00000-09-00-0638 and B00000-09-00-0640. It seems that the signal SV 8622_ OPEN appears on both drawings (slot0-channel 6 in B00000-09-00-0638 and slot2- channel 1 in B00000-09-00-0640 ). I'd like to know if these are correct?. 

On the other hand when compared the spreadsheets for the local and remote solenoid PLCs with the drawings there was some mismatch: 
- Drawing B00000-09-00-0623 local/chassis- slot 0- channel 6 shows the HALL_SENSOR connected and it is missed on the spreadsheet. 
- Drawing B00000-09-00-0645 remote/chassis-slot 7: seems to have 3 spares in channels 5,4 and 3; but the spreadsheet doesn't show the same. 




Best Regards 
Pablo Campero 
Detector Support Group. 