[Halld-controls] [EXTERNAL] BCAL Chiller Comm. -PLC control troubleshoot

Hovanes Egiyan hovanes at jlab.org
Tue Jan 10 13:41:58 EST 2023


Brian, could you send me the PLC tag names for the variables that switch the assignment of the BCAL chillers. We might be able to do it from EPICS GUIs in the future.

Thanks a lot,
        Hovanes.

________________________________
From: Brian Eng <beng at jlab.org>
Sent: Tuesday, January 10, 2023 12:57 PM
To: Scot Spiegel <spiegel at jlab.org>
Cc: Hovanes Egiyan <hovanes at jlab.org>; halld-controls at jlab.org <halld-controls at jlab.org>
Subject: Re: [Halld-controls] [EXTERNAL] BCAL Chiller Comm. -PLC control troubleshoot

I changed the DS to use #3, it just needs to now actually be online.

> On Jan 10, 2023, at 12:53 PM, Scot Spiegel <spiegel at jlab.org> wrote:
>
> #3 is the current one installed
>
> Get Outlook for iOS
> From: Halld-controls <halld-controls-bounces at jlab.org> on behalf of Hovanes Egiyan via Halld-controls <halld-controls at jlab.org>
> Sent: Tuesday, January 10, 2023 12:49:47 PM
> To: Brian Eng <beng at jlab.org>
> Cc: halld-controls at jlab.org <halld-controls at jlab.org>
> Subject: Re: [Halld-controls] [EXTERNAL] BCAL Chiller Comm. -PLC control troubleshoot
>
> According to Nick, the code should switch the DS chiller to become chiller #3 when we swap #2 to #3.
>
>
>
> Sent from my Galaxy
>
>
>
> -------- Original message --------
> From: Brian Eng <beng at jlab.org>
> Date: 1/10/23 12:45 PM (GMT-05:00)
> To: Hovanes Egiyan <hovanes at jlab.org>
> Cc: "hovanes.egiyan" <hovanes.egiyan at gmail.com>, halld-controls at jlab.org
> Subject: Re: [Halld-controls] [EXTERNAL] BCAL Chiller Comm. -PLC control troubleshoot
>
> Yeah, I had used the .ACD from there.
>
> Looks like it's trying to communicate with 3 watlows, only one of them is online (responds to pings) now.
>
> .26.190 = 1 = online
> .26.189 = 2 = offline
> .26.215 = 3 = offline
>
> Currently the US is set to use 1 and the DS is set to use 2.
>
>
> P.S. The COMCAL watlow is also offline.
>
> > On Jan 10, 2023, at 12:14 PM, Hovanes Egiyan <hovanes at jlab.org> wrote:
> >
> > Brian,
> >
> > here is the location of that L5X file, that is the last one I got from Nick:
> >
> > https://halldsvn.jlab.org/repos/trunk/controls/plc/reset/l5x/HallD_HV_Reset.L5X
> >
> > Hovanes.
> >
> >
> > From: Halld-controls <halld-controls-bounces at jlab.org> on behalf of Brian Eng via Halld-controls <halld-controls at jlab.org>
> > Sent: Tuesday, January 10, 2023 11:46 AM
> > To: hovanes.egiyan <hovanes.egiyan at gmail.com>
> > Cc: halld-controls at jlab.org <halld-controls at jlab.org>
> > Subject: Re: [Halld-controls] [EXTERNAL] BCAL Chiller Comm. -PLC control troubleshoot
> >
> > I figured that the comms would go through a PLC, I'm just not sure which it is.
> >
> > BCAL_DS = .26.22
> > BCAL_US = .26.23
> >
> > Both of these PLCs are trying to set the channel that corresponds to the chiller remote signal to 1.
> >
> > I don't know what RESET corresponds to.
> >
> > > On Jan 10, 2023, at 11:22 AM, hovanes.egiyan <hovanes.egiyan at gmail.com> wrote:
> > >
> > > The IOC for BCAL chiller is called RESET PLC IOC or CRATE RESET IOC or something. There is no direct EPICS to chiller communication now. RESET is the name of the PLC in question.
> > > Rebooting this IOC will trip FDC chiller.
> > >
> > >
> > >
> > > Sent from my Galaxy
> > >
> > >
> > > -------- Original message --------
> > > From: Brian Eng via Halld-controls <halld-controls at jlab.org>
> > > Date: 1/10/23 10:01 AM (GMT-05:00)
> > > To: Scot Spiegel <spiegel at jlab.org>, halld-controls at jlab.org
> > > Subject: Re: [Halld-controls] BCAL Chiller Comm. -PLC control troubleshoot
> > >
> > > Hovanes,
> > >
> > > I'm assuming that EPICS is trying to communicate with a PLC, do you know the hostname/IP for this?
> > >
> > > I tried connecting to the US/DS BCAL PLCs but don't see any actual communications with a chiller, only an interlock signal.
> > > From: Scot Spiegel <spiegel at jlab.org>
> > > Sent: Tuesday, January 10, 2023 9:00 AM
> > > To: Brian Eng <beng at jlab.org>; halld-controls at jlab.org <halld-controls at jlab.org>
> > > Cc: Timothy Whitlatch <whitey at jlab.org>; Bobby Bunton <bunton at jlab.org>
> > > Subject: Re: BCAL Chiller Comm. -PLC control troubleshoot
> > >
> > > Ok, just let me know. Thanks, Scot
> > >
> > > Get Outlook for iOS
> > > From: Brian Eng <beng at jlab.org>
> > > Sent: Tuesday, January 10, 2023 8:58:36 AM
> > > To: Scot Spiegel <spiegel at jlab.org>; halld-controls at jlab.org <halld-controls at jlab.org>
> > > Cc: Timothy Whitlatch <whitey at jlab.org>; Bobby Bunton <bunton at jlab.org>
> > > Subject: Re: BCAL Chiller Comm. -PLC control troubleshoot
> > >
> > > Just got my JLab account unlocked.
> > >
> > > Let me see if I can connect with the computer on Hall D that has PLC software installed, I don't think I've tested it with the BCAL stuff.
> > > From: Scot Spiegel <spiegel at jlab.org>
> > > Sent: Tuesday, January 10, 2023 8:28 AM
> > > To: halld-controls at jlab.org <halld-controls at jlab.org>; Brian Eng <beng at jlab.org>
> > > Cc: Timothy Whitlatch <whitey at jlab.org>; Bobby Bunton <bunton at jlab.org>
> > > Subject: BCAL Chiller Comm. -PLC control troubleshoot
> > >
> > > Brian,
> > >
> > > I'm requesting some support in Hall D to TS the remote controls of the BCAL chiller #3 temperature controller.
> > >
> > > Currently our Logix 5000 Laptop is in IT being updated. Would you be available to help Bobby Bunton with this?
> > >
> > > Thanks,
> > >
> > > Scot Spiegel
> > >
> > > Hall D Work Coordinator
> > > Phone 757-876-3940
> > >
> > > Physics Division
> > >
> > > JSA Jefferson Lab
> > > 12000 Jefferson Ave.
> > > Bldg. 55 Rm. 2564
> > > Newport News, VA. 23606
> > >
> > > Technical Phone X 5900
> > > Mobile Phone 757-536-5900
> >
> >
> > _______________________________________________
> > Halld-controls mailing list
> > Halld-controls at jlab.org
> > https://mailman.jlab.org/mailman/listinfo/halld-controls

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/halld-controls/attachments/20230110/80a5ca4e/attachment-0001.html>


More information about the Halld-controls mailing list