[Rich] [Dsg-rich] FPGA temp alarm

Chris Cuevas cuevas at jlab.org
Tue Oct 16 14:53:02 EDT 2018


Hi Tyler,

So the cRIO software must always be running to detect out of limit 
signals from the front end sensors? What happens if the software stops 
running? Is there a default timeout[watchdog] setting that will open the 
final relay contact?

Thanks for the feedback,

-Chris

~~~~~~~~~~~


On 10/16/2018 1:52 PM, Tyler Lemon wrote:
> Chris,
>
> For the hardware interlocks, if any of the cRIO-based system's sensors 
> (RTDs, humidity, airflow, air pressure, N2 flow; sensors not dependent 
> on FPGA DAQ readout) go out of limit, the cRIO disables HV and LV by 
> opening a relay contact to the Interlock port on the CAEN mainframe.
>
> This disables HV and LV and will only allow HV and LV to be re-enabled 
> if the interlock is clear and a user has reset the interlock.
>
> Regards,
> Tyler
>
>
>
>
> ------------------------------------------------------------------------
> *From: *"Chris Cuevas" <cuevas at jlab.org>
> *To: *"Valery Kubarovsky" <vpk at jlab.org>, "Mirazita Marco" 
> <Marco.Mirazita at lnf.infn.it>
> *Cc: *rich at jlab.org, "dsg-rich" <dsg-rich at jlab.org>
> *Sent: *Tuesday, October 16, 2018 1:38:14 PM
> *Subject: *Re: [Rich] [Dsg-rich] FPGA temp alarm
>
> Hi All,
>
> The FPGAs have a firmware set point for the die temperature. Ben can 
> verify this set point, but it sure sounds like the 'interlock' systems 
> rely on software code. Are there watchdog timers set up in case the 
> code stops running?
>
> For a true hardware interlock, one that does not depend on software, 
> there should be temperature probes coupled directly to a comparator 
> circuit which latches off the Low_Voltage outputs to the FPGA boards. 
> From these email threads, it sounds like all the temperature devices 
> are monitored with software, and if a software set point threshold is 
> violated, then the Low_Voltage is turned OFF. If the monitored 
> temperature devices go below the software set point threshold, is the 
> Low_Voltage power reapplied automatically?
>
> Thanks,
>
> -Chris
>
> ~~~~~~~~~~~~~~~~~
>
>
> On 10/16/2018 9:40 AM, Valery Kubarovsky wrote:
>
>     The detector (actually LV in this particular case, because the HV
>     was off at that moment)
>     was shut down by software interlock that monitors the FPGS
>     temperature.
>
>     ------------------------------------------------------------------------
>
>         *From: *"Marco Mirazita" <Marco.Mirazita at lnf.infn.it>
>         *To: *"Tyler Lemon" <tlemon at jlab.org>
>         *Cc: *"Valery Kubarovsky" <vpk at jlab.org>, rich at jlab.org,
>         "dsg-rich" <dsg-rich at jlab.org>
>         *Sent: *Tuesday, October 16, 2018 9:37:41 AM
>         *Subject: *Re: [Rich] [Dsg-rich] FPGA temp alarm
>
>         But we have a soft interlock shutting down the system if fpga
>         temperature goes above 75 deg.
>
>
>         Il 2018-10-16 14:24 Tyler Lemon ha scritto:
>         > Hello Marco,
>         >
>         > The hardware interlock system does not monitor FPGA
>         temperatures. It
>         > monitors the RTDs installed in the EP.
>         >
>         > The hardware interlock system did not trip off the
>         electronics because
>         > the strange temperature readings were only seen on the FPGA
>         > temperature readouts.
>         >
>         > Best regards,
>         > Tyler
>         >
>         > -------------------------
>         >
>         > FROM: "Mirazita Marco" <Marco.Mirazita at lnf.infn.it>
>         > TO: "Valery Kubarovsky" <vpk at jlab.org>
>         > CC: rich at jlab.org, "dsg-rich" <dsg-rich at jlab.org>
>         > SENT: Tuesday, October 16, 2018 8:16:06 AM
>         > SUBJECT: Re: [Rich] [Dsg-rich] FPGA temp alarm
>         >
>         > Hi Valery,
>         > thank you, in fact my main worry was that the interlock
>         didn't shut
>         > down
>         > the electronics.
>         > It would be anyway good to understand why we had this event.
>         > I saw from the strip charts that also the LV currents and
>         voltages
>         > have
>         > frequent random spikes.
>         > Marco
>         >
>         > Il 2018-10-16 13:55 Valery Kubarovsky ha scritto:
>         >> Marco,
>         >> If you take a more careful look you will find out that the
>         LV was
>         > shut
>         >> down.
>         >> The HV was off. We investigate the reason. It is the first
>         time we
>         > had
>         >> such an event.
>         >> Probably it was connected with the software update that was
>         done
>         >> approximately at the same time.
>         >> Regards,
>         >> Valery
>         >>
>         >> -------------------------
>         >>
>         >>> FROM: "Marco Mirazita" <Marco.Mirazita at lnf.infn.it>
>         >>> TO: dsg-rich at jlab.org, rich at jlab.org
>         >>> SENT: Tuesday, October 16, 2018 4:03:24 AM
>         >>> SUBJECT: [Dsg-rich] FPGA temp alarm
>         >>
>         >>> Hi all,
>         >>> yesterday at about 4:20 pm jlab time I received several alarm
>         >>> messages
>         >>> saying that the FPGA temperatures reached values around
>         115 deg.
>         >>> Since it looked like a readout error, I checked the strip
>         chart,
>         >>> where
>         >>> there is actually a spike in the readout at that time, but to
>         > values
>         >>> of
>         >>> the order of -10^5. See the attached plot.
>         >>> So, it is clear that it was a readout error, but it is
>         strange that
>         >>> the
>         >>> alarm message and epics report different values.
>         >>> Also, according to the logbook, the electronics was not
>         shut down
>         > by
>         >>> the
>         >>> interlocks, as should have happened if the temperature
>         really went
>         >>> above
>         >>> 100 deg.
>         >>> So, perhaps the values reported in the alarm messages are
>         not the
>         >>> correct ones?
>         >>> Marco
>         >>>
>         >>> _______________________________________________
>         >>> Dsg-rich mailing list
>         >>> Dsg-rich at jlab.org
>         >>> https://mailman.jlab.org/mailman/listinfo/dsg-rich
>         >>
>         >> _______________________________________________
>         >> Dsg-rich mailing list
>         >> Dsg-rich at jlab.org
>         >> https://mailman.jlab.org/mailman/listinfo/dsg-rich
>         > _______________________________________________
>         > Rich mailing list
>         > Rich at jlab.org
>         > https://mailman.jlab.org/mailman/listinfo/rich
>
>
>
>     _______________________________________________
>     Rich mailing list
>     Rich at jlab.org
>     https://mailman.jlab.org/mailman/listinfo/rich
>
>
>
> _______________________________________________
> Rich mailing list
> Rich at jlab.org
> https://mailman.jlab.org/mailman/listinfo/rich