[Testlablcwusers] Energizing MOLLER TM1 to 2453 A
Mike Drury
drury at jlab.org
Wed Nov 5 09:00:10 EST 2025
We are usually running from 9AM - 10PM weekdays. We have a week to a
week and a half of testing to do.
Mike D.
On 11/5/2025 7:03 AM, Philip Denny wrote:
> Hello Eric,
>
> I cannot see who is on the "testlablcwusers at jlab.org" mail list. But
> we need to add Mike Drury and Mike McCaughan if they are not.
>
> There is currently a CEBAF cryomodule in the test cave being tested. I
> cannot comment when it will be completed, nor the typical daily hours
> they are running the high power supply that may (most likely) is
> affecting the water temp.
>
> The following statement has been communicated to us: /"C//MTF / VTA
> have priority per lab management in event of conflicts. We are the
> long poles in the tent to maintain the CEBAF start-up schedule, which
> was communicated to them in their work planning document. Doug
> Higinbotham can mediate for the SAM planning committee in the event
> this becomes an issue."/
> /
> /
> Hopefully between you and Mike and Mike, you can work something out as
> far as timing.
>
> Phil
> /
> /
> /
> /
>
>
>
>
> ------------------------------------------------------------------------
> *From:* Testlablcwusers <testlablcwusers-bounces at jlab.org> on behalf
> of Eric Sun <qsun at jlab.org>
> *Sent:* Tuesday, November 4, 2025 2:47 PM
> *To:* testlablcwusers at jlab.org <testlablcwusers at jlab.org>
> *Cc:* John Fischer <fischer at jlab.org>
> *Subject:* [Testlablcwusers] Energizing MOLLER TM1 to 2453 A
> Howdy,
>
> We will ramp our MOLLER TM1 magnet up to 2453 A this week starting
> from now. We will ramp it to 2230 A operating current first. The heat
> that will be dumped into the LCW system is about 90 kW. The required
> flow rate of LCW is 10 gallons per minute.
>
> Thanks a lot for attention.
>
> Eric Sun
> MOLLER
>
-------------- next part --------------