My previous email was inaccurate.
We will not ramp our TM3 magnet up to 4000 A. We will ramp it to 3370 A operating current. The heat that will be dumped into the LCW system will be about 110 kW. The required flow rate of LCW is 23 gallons per minute.
Thanks
Eric
________________________________
From: Testlablcwusers <testlablcwusers-bounces at jlab.org> on behalf of Eric Sun <qsun at jlab.org>
Sent: Tuesday, October 14, 2025 10:36 AM
To: testlablcwusers at jlab.org <testlablcwusers at jlab.org>
Subject: Re: [Testlablcwusers] We plan to ramp MOLLER TM3 to 3710 A now
Howdy,
We plan to continue the power-up test of MOLLER TM3 magnet at the Test Lab from morning (10:30 AM) 10/14/2025 to 10/17/2025. The testing will be on and off. We will test the magnet up to 4000 A. The maximum power consumption of the magnet is 138 kW. The required flow rate of LCW is 23 gallons per minute.
If you have any concerns, please contact me ASAP.
Many thanks for the attention.
Cheers
Eric
________________________________
From: Eric Sun
Sent: Wednesday, October 1, 2025 9:56 AM
To: testlablcwusers at jlab.org <testlablcwusers at jlab.org>
Subject: We plan to ramp MOLLER TM3 to 3710 A now
Hi,
We plan to ramp MOLLEZR TM3 to 3710 A now. The magnet will consume 138 kW. The required flow rate will be about 40 GPM.
Thanks a lot
Eric