[Clas12_rich] RICH Detector Cooling Circuit Pressure System Considerations
George Jacobs
jacobsg at jlab.org
Thu May 19 09:16:32 EDT 2016
Hi Saptarshi,
The high pressure section of the system is at 125 psi, from the
compressor output to the air tank. Pressure is reduced at the tank
outlet to 55 psi or less by a pressure regulator to supply air to the
detector air flow control valve. After that, it discharges to the the
electronics enclosure inside the detector.
There are 3 relief valves in the system;
Relief valve #1 for the ASME air tank
Relief valve #2 and #3 for the detector air supply
I do not know who will do the procurement or when it is planned for. I
have attached a spreadsheet with the list of known components for the
cooling system.
George
On 5/18/2016 8:58 AM, Saptarshi Mandal wrote:
> George,
>
> Do you know the pressure in the tank for this system and also the max.
> working pressure ? Are we procuring the tank, relief valves,
> regulators or is the RICH group providing these ?
>
> Thanks.
> Saptarshi
>
> On 5/12/2016 1:49 PM, George Jacobs wrote:
>> Hi Bob,
>>
>> This is a heads up for the RICH detector cooling circuit which cools
>> the electronics package inside the detector. This piping system
>> requires some pressure system analysis. I do not know the time line
>> on this project.
>>
>> Please see attached PDF file detailing the RICH detector cooling
>> circuit for the internal electronics package.
>>
>> There are 3 relief valves in the system;
>> Relief valve #1 for the ASME air tank
>> Relief valve #2 and #3 for the detector air supply
>>
>> The high pressure section of the system is at 125 psi from the
>> compressor output charging the air tank. Pressure is reduced at the
>> tank outlet to 55 psi or less by a pressure regulator to supply air
>> to the detector air flow control valve. After that, it discharges to
>> the the electronics enclosure inside the detector.
>>
>> George
>>
>
--
George Jacobs
Jefferson Lab (TJNAF)
STE 12
12000 Jefferson Ave.
Newport News, VA 23606
(office) 757-269-7115
(cell) 757-876-0480
(email) jacobsg at jlab.org
(website) https://userweb.jlab.org/~jacobsg
-------------- next part --------------
A non-text attachment was scrubbed...
Name: RICH-Cooling-Circuit-Costs.xls
Type: application/vnd.ms-excel
Size: 29184 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/clas12_rich/attachments/20160519/821dd460/attachment-0001.xls>
More information about the Clas12_rich
mailing list