[Dsg-hallbgas] [Dsg-mvt] MVT mass flow controller set points
Marc McMullen
mcmullen at jlab.org
Wed Mar 14 16:49:07 EDT 2018
Amrit,
I concur with this assessment. If there is a scheduled maintenance
involving controlled gas supplies, DSG should be informed so that the
appropriate measures can be applied prior to an outage. In addition to
your MFC accounting I would like to add that there is only one spare
cRIO for the gas system.
We will look into adding an alarm based on the value of the MFC
initialization, this would provide an alert if the MFC software is
stopped due to a communications failure between the cRIO and any of the
associated MFCs.
Thanks,
Marc
On 3/14/2018 4:09 PM, Amrit Yegneswaran wrote:
> marc with regards to your e-mail, here are some clarifications.
>
> 1. @ 0801 hrs SVT MFCs on the space frame were disconnected by Hall B
> engineering, which is why the cRIO on the space frame hung up.
> 2. @ ~1030 hrs gotra noted the gas wasn't flowing to the SVT and
> contacted peter.
> 3. tyler, pablo, amanda, marc restored the cRIO at ~1100 hrs.
> 4. so, the MVT was without gas for ~3 hours.
>
> Recommendations:
>
> 1. Hall B detector managers should be informed and should inform
> their counterparts via the mailing lists prior to any work on /any
> component/ of the the gas system, so that t appropriate measures
> can be taken to ensure the safety of the detector.
> 2. MVT and HTCC /should invest/ in owning their own cRIO system, so
> that all systems are independent, see table.
>
> cRIO location
> Systems
> #of MFCs
> Available spares
>
> SVT
> 1 to 3
> 0
> Space Frame
> MVT
> 5
> 3
>
> HTCC
> 1
> 0
>
>
>
>
> Forward Carriage
> LTCC
> 4
> 2
>
>
>
>
> Gas Shed
> DC mixing system
> 4
> 1
>
> DC supplies
> 3
>
>
>
>
>
>
>
>
>
> ------------------------------------------------------------------------
> *From: *"Marc Mcmullen" <mcmullen at jlab.org>
> *To: *"Maxime Defurne" <mdefurne at jlab.org>, dsg-mvt at jlab.org,
> dsg-hallbgas at jlab.org
> *Cc: *"Bob Miller" <rmiller at jlab.org>
> *Sent: *Wednesday, March 14, 2018 12:46:45 PM
> *Subject: *Re: [Dsg-mvt] MVT mass flow controller set points
>
> Maxime,
>
> I am passing this information to the Hall B Gas community. Some work was
> done to some of the mass flow controllers which are on the same cRIO as
> the MVT. The gas system has been designed with a fix for mfc related
> issues, so during some circumstances someone who is on-call may be
> required to reboot one of the cRIOs, to reset the mfc software.
>
> Additional training needs to be conducted if this is a potential problem
> for the MVT. I will bring this up during our meeting, please talk with
> Bob and Stepan so this information is known to all.
>
> -Marc
>
>
> On 3/14/2018 12:32 PM, mdefurne wrote:
> > Hi Marc,
> >
> > Everything is fine (Mixture ratio and flow).
> >
> > But next time, please tell us before rebooting the cRIO so that we do
> > not take any risk (HV was on and if something would not have been good
> > with the gas for any reason, it would have been a disaster). I got a
> > bit scared when I read your e mail :P
> >
> > Cheers,
> >
> > Maxime
> >
> >
> > Le 14/03/2018 à 12:24, Marc McMullen a écrit :
> >> Hi Maxime,
> >>
> >> We had to reboot the cRIO which controls all the mfc for the space
> >> frame, including the mixing system for mvt. Please check your set
> >> points, and manual/automatic settings to ensure you are getting the
> >> desired flow.
> >>
> >>
> >
> > _______________________________________________
> > Dsg-mvt mailing list
> > Dsg-mvt at jlab.org
> > https://mailman.jlab.org/mailman/listinfo/dsg-mvt
>
> --
> Marc McMullen
> Detector Support Group
> 757-269-7738
>
> _______________________________________________
> Dsg-mvt mailing list
> Dsg-mvt at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-mvt
> G
> M
> T
>
>
> Text-to-speech function is limited to 200 characters
> Options
> <moz-extension://9a02252d-fe80-4f21-89c6-673418b2428d/content/html/options/options.html?bbl>
> : History
> <moz-extension://9a02252d-fe80-4f21-89c6-673418b2428d/content/html/options/options.html?hist>
> : Feedback
> <moz-extension://9a02252d-fe80-4f21-89c6-673418b2428d/content/html/options/options.html?feed>
> : Donate
> <https://www.paypal.com/cgi-bin/webscr?cmd=_s-xclick&hosted_button_id=GD9D8CPW8HFA2>
> Close
>
--
Marc McMullen
Detector Support Group
757-269-7738
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_gas/attachments/20180314/461bf0da/attachment-0002.html>
More information about the Dsg-hallbgas
mailing list