Hello Pablo,
The description and calculations looks good to me, but the PLC tag for comparators (C1, C2 etc.) are confusing! Normally C is used for coil, but these are not the coils!
Could you suggest some other name (may be COMP1 etc.).
Thanks
Renuka
----- Original Message -----
From: "Pablo Campero" <campero at jlab.org>
To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
Sent: Thursday, December 1, 2016 5:00:46 PM
Subject: [Dsg-hallb_magnets] Solenoid- PLC software comparators
Hello Wesley, 
Attached table with the PLC tag name for the Solenoid software comparators and voltages. 
You can also find this spreadsheet in the M Drive, the path is M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring Solenoid PLC Software Comparators 
Renuka, 
Let me know if you have any correction in the attached table, I assigned the voltage (V1 to V15 ) and comparators (C1 to C10) based on your "Hall-B Solenoid Quench Detector Channel Assigment and Voltage Limits QD and Software" spread sheet. 
Thanks 
Pablo Campero 
Detector Support Group. 